Hi All,
We have been doing Transformer Stability tests at our project.
The System details are:
Transformer - 34.5kV/.480kV,Delta-Star,3Ph,60Hz
The Transformer Secondary Neutral point is connected to Earth through a High Resistance Ground Unit.
A typical Transformer Differential protection scheme is applied.
For testing the diffrential scheme-we apply a reduced voltage of 480V on the Transformer Primary.
The Secondary bus is shorted. A current equivalent to the rated primary current is forced to flow through the transformer primary winding.
At this condition we measure the Secondary current.
However we noted that the measured Secondary current is much less than the rated Secondary current.
Does this mean that the % Transformer Impedance is not correct
Z=6.75% in this case.
Or is it that the % Transformer impedance is applicable to its rated primary Voltage and will vary based on the applied Primary voltage?
Please guide me.
Thank you
We have been doing Transformer Stability tests at our project.
The System details are:
Transformer - 34.5kV/.480kV,Delta-Star,3Ph,60Hz
The Transformer Secondary Neutral point is connected to Earth through a High Resistance Ground Unit.
A typical Transformer Differential protection scheme is applied.
For testing the diffrential scheme-we apply a reduced voltage of 480V on the Transformer Primary.
The Secondary bus is shorted. A current equivalent to the rated primary current is forced to flow through the transformer primary winding.
At this condition we measure the Secondary current.
However we noted that the measured Secondary current is much less than the rated Secondary current.
Does this mean that the % Transformer Impedance is not correct
Z=6.75% in this case.
Or is it that the % Transformer impedance is applicable to its rated primary Voltage and will vary based on the applied Primary voltage?
Please guide me.
Thank you