GasProcess
Petroleum
- Oct 14, 2003
- 33
We are replacing some isolation valve on the sea water cooling pipe lines size ranging 6" to 36". Due to some mix-up, the valves which are ordered as replacement are of 125 class Flat Face, where as existing valves and flanges are of 150 class Raised Face. We do not want to cut and replace the RF flanges to install the new FF valves due to internal coating on the pipe.
- Could some one please suggest if it is ok to use full face flat gasket for this situation i.e. RF pipe Flanges with FF valves in between them?
- Do we have to insert metallic annular spacer equal to the thickness of the raised face ( 1.6 mm ) to fill the gap created due to RF on the pipe flange? This spacer may provide necessary support to the FF flange.
- Will proper sealing be made to hold the 60 psig pressure.
- Does this situation violate any piping code? Appendix 'Y' of ASME div-1 sec. VIII allows spacer between the FF flanges.
- Is it technically feasible to fabricate spacer with thickness 1.6 mm?
- Could some one please suggest if it is ok to use full face flat gasket for this situation i.e. RF pipe Flanges with FF valves in between them?
- Do we have to insert metallic annular spacer equal to the thickness of the raised face ( 1.6 mm ) to fill the gap created due to RF on the pipe flange? This spacer may provide necessary support to the FF flange.
- Will proper sealing be made to hold the 60 psig pressure.
- Does this situation violate any piping code? Appendix 'Y' of ASME div-1 sec. VIII allows spacer between the FF flanges.
- Is it technically feasible to fabricate spacer with thickness 1.6 mm?