I was at a project site on Friday and saw some interesting voltage measurements that I would be interested if anybody could explain. Now, I know these aren't mathematically possible, but I saw them, other saw them, and they had been reported the day prior, which is why I went to the site; so nobody need respond that there was an error in the readings.
The relevant portion of the system begins with a 480V delta transformer winding. The three phase from this transformer are fed into some 480V switchgear. Also connected to the switchgear, but not running (and breakers open) are three generators which can be run parallel to the utility, that's why the delta winding. Connected to the 480V bus are a set of 277V-120V grounded-wye/grounded-wye VTs (yes, they should be 480V-120V and that will be corrected but that shouldn't matter for this). The output of the VTs are connected to a CAT/ISO control module, an Eaton Power Meter, and an SEL-351 relay. The control module has only phases A and C connected plus the neutral of the VTs. The Eaton Power Meter has the three phase voltages input and has a separate ground connection. The SEL-351 relay has all three phases and neutral connected. All three devices have a VT ratio of 2.31 programmed in. The SEL relay and the Eaton Power Meter report about 281V line to ground/neutral for all three phases as could be expected. So far, so good.
Now the problem; the CAT/ISO control module reports 148V secondary/342V primary. OK, that's easy - a bad module. Well, if only it were that easy. Two different Fluke DMMs were used to make measurements (I didn't get the model numbers, both had calibration stickers indicating calibration in 2006) and this is where it gets very interesting. Measuring on the bus of the 480V gear, the Flukes read 485V to 490V across each of the three phase pairs - completely reasonable, and an indication that the meter isn't wildly off. They also read between 340V and 345V phase to ground. On the secondary of the VTs, the Fluke meters read 210V to 215V phase to phase and between 145V and 150V phase to neutral.
I had the thought that on this ungrounded system, the Fluke meter was somehow causing a neutral shift, but a couple of tests tend to disprove that. One test was having both Fluke meters used at the same time, one A to ground and one C to ground, and they both read about 348V. Another test was measuring the voltages at the terminals on the rear of the SEL relay while watching the metering display on the front of the relay. With a VT ratio of 2.31 programmed into the relay, and a metering display of 281V phase to neutral (primary), the relay thinks that it has 122V applied to the terminals. Measuring across the same terminals with the Fluke meter, the fluke read 148V and the metering display on the relay did not change.
Any ideas? The voltages listed above were all read from the devices indicated by more than one person. One oscillographic record was trigged and downloaded and it showed that there was between 119[°] and 121[°] between phases, so that isn't the cause either.
The relevant portion of the system begins with a 480V delta transformer winding. The three phase from this transformer are fed into some 480V switchgear. Also connected to the switchgear, but not running (and breakers open) are three generators which can be run parallel to the utility, that's why the delta winding. Connected to the 480V bus are a set of 277V-120V grounded-wye/grounded-wye VTs (yes, they should be 480V-120V and that will be corrected but that shouldn't matter for this). The output of the VTs are connected to a CAT/ISO control module, an Eaton Power Meter, and an SEL-351 relay. The control module has only phases A and C connected plus the neutral of the VTs. The Eaton Power Meter has the three phase voltages input and has a separate ground connection. The SEL-351 relay has all three phases and neutral connected. All three devices have a VT ratio of 2.31 programmed in. The SEL relay and the Eaton Power Meter report about 281V line to ground/neutral for all three phases as could be expected. So far, so good.
Now the problem; the CAT/ISO control module reports 148V secondary/342V primary. OK, that's easy - a bad module. Well, if only it were that easy. Two different Fluke DMMs were used to make measurements (I didn't get the model numbers, both had calibration stickers indicating calibration in 2006) and this is where it gets very interesting. Measuring on the bus of the 480V gear, the Flukes read 485V to 490V across each of the three phase pairs - completely reasonable, and an indication that the meter isn't wildly off. They also read between 340V and 345V phase to ground. On the secondary of the VTs, the Fluke meters read 210V to 215V phase to phase and between 145V and 150V phase to neutral.
I had the thought that on this ungrounded system, the Fluke meter was somehow causing a neutral shift, but a couple of tests tend to disprove that. One test was having both Fluke meters used at the same time, one A to ground and one C to ground, and they both read about 348V. Another test was measuring the voltages at the terminals on the rear of the SEL relay while watching the metering display on the front of the relay. With a VT ratio of 2.31 programmed into the relay, and a metering display of 281V phase to neutral (primary), the relay thinks that it has 122V applied to the terminals. Measuring across the same terminals with the Fluke meter, the fluke read 148V and the metering display on the relay did not change.
Any ideas? The voltages listed above were all read from the devices indicated by more than one person. One oscillographic record was trigged and downloaded and it showed that there was between 119[°] and 121[°] between phases, so that isn't the cause either.