Gentlemen,
I am involved in a HRSG project in the Middle East that makes extensive use of ASME P91 (A335, A234 and A182).
As a result of concerns over weld quality, the contractor has appointed an inspection company to make hardness measurements on all pipe to pipe and pipe to branch welds and on the base metal of all elbows. The measurements have been made using a portable tester supplied by Sievert. In addition, the measurements have been made 3 times at the each of 3 and 9 o'clock positions and this has been repeated at the following planes across the weld;
namely, base metal then HAZ then weld surface then HAZ then base metal.
To assist in the interpretation of the results, the contractor advised that the acceptable range of hardness was 190 to 300HV. Unfortunately, the inspection company applied a range of 180 to 300HV stating that 180HV is the min required by standards.
To complicate matters the contractor had previously submitted procedures for N&T and PWHT which gave different acceptable ranges. The N&T procedure gives a range of 220 to 263HV whereas the PWHT procedure give 200 to 263HV for the base metal and 200 to 263HV for the weld and HAZ.
For the pipe to pipe and pipe to branch welds the measured results are:
Base metal 185 to 280HV
HAZ 153 to 310HV
Weld 240 to 480HV
At this time the contractor is not proposing any remedial measures for welds where the:
base metal hardness is less than 200HV or more than 263HV,
HAZ hardness is less than 200HV,
weld hardness is more than 320HV.
In addition, the contractor is not proposing any remedial measures where the base metal, HAZ or welds have hardness less than 180HV.
For the elbows, the measured base metal hardness are 153 to 210HV. The contractor is proposing to remove and re-N&T all elbows with base metal hardness less than 180HV.
It is my opinion, that the contractor should undertake remedial works where the hardness values are outside the N&T and PWHT procedures as these were agreed before there were concerns over weld quality. I am just a little suspicious that the limits in the hardness measurement were selected to minimise the scope of remedial works.
I would appreciate any technical comments on the measured hardness values and the acceptance limits being applied.
Best Regards,
athomas236
I am involved in a HRSG project in the Middle East that makes extensive use of ASME P91 (A335, A234 and A182).
As a result of concerns over weld quality, the contractor has appointed an inspection company to make hardness measurements on all pipe to pipe and pipe to branch welds and on the base metal of all elbows. The measurements have been made using a portable tester supplied by Sievert. In addition, the measurements have been made 3 times at the each of 3 and 9 o'clock positions and this has been repeated at the following planes across the weld;
namely, base metal then HAZ then weld surface then HAZ then base metal.
To assist in the interpretation of the results, the contractor advised that the acceptable range of hardness was 190 to 300HV. Unfortunately, the inspection company applied a range of 180 to 300HV stating that 180HV is the min required by standards.
To complicate matters the contractor had previously submitted procedures for N&T and PWHT which gave different acceptable ranges. The N&T procedure gives a range of 220 to 263HV whereas the PWHT procedure give 200 to 263HV for the base metal and 200 to 263HV for the weld and HAZ.
For the pipe to pipe and pipe to branch welds the measured results are:
Base metal 185 to 280HV
HAZ 153 to 310HV
Weld 240 to 480HV
At this time the contractor is not proposing any remedial measures for welds where the:
base metal hardness is less than 200HV or more than 263HV,
HAZ hardness is less than 200HV,
weld hardness is more than 320HV.
In addition, the contractor is not proposing any remedial measures where the base metal, HAZ or welds have hardness less than 180HV.
For the elbows, the measured base metal hardness are 153 to 210HV. The contractor is proposing to remove and re-N&T all elbows with base metal hardness less than 180HV.
It is my opinion, that the contractor should undertake remedial works where the hardness values are outside the N&T and PWHT procedures as these were agreed before there were concerns over weld quality. I am just a little suspicious that the limits in the hardness measurement were selected to minimise the scope of remedial works.
I would appreciate any technical comments on the measured hardness values and the acceptance limits being applied.
Best Regards,
athomas236