raithrovers1

Industrial
Feb 10, 2009
85
I have an engineer that has come back from a site with the waveforms from a 50KVA UPS that were captured on his scope. The phase to phase waveform is sinusoidal without a great deal of distortion. The unit did not seem to be loaded anywhere near the system capabilities but the engineer did not check the crest factor of the load.
However, the phase to neutral waveform is almost triangular in shape on all three phases. Any ideas why the phase to phase voltage is OK but the phase to neutral waveform is so distorted?

UPS Service Manager
 
Replies continue below

Recommended for you

Third-tone injection is a common technique to get full phase-phase voltage. But this does not sound quite like that. What do your other UPS-es look like?

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
OK. Better talk to the manufacturer then.
I still think it is in good order and that the third tone injection is causing the waveform. No need to worry, I think.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 