Hi
I am working on selecting a pressure booster pump for a small residential apartment building. I am estimating my peak cold water demand based in the Water Supply Fixture Units, from the American Society of Plumbing Engineering Design Handbook Vol2, Tables 5-18 & 5-19. I'm using the values for combined the hot & cold water because cold water will be fed into standalone water heaters in each apartment, so the hot water demand is ultimately cold water demand. (hope that doesn't sound too confusing)
I have 11 identical flats, each has the following water demand outlets:
2 water closets: 2 x 2.2 = 4.4 WSFU
2 Wash Basins: 2 x 3 = 6.0 WSFU
1 Bathtub: 1.4 WSFU
2 Hand Bidet: 2 x 1 = 2 WSFU (Not in the table, estimated)
1 Kitchen Sink: 1.4 WSFU
Total for 1 apartment = 15.2 WSFU
Total for building = 15.2 x 11 = 167.2 WSFU
From the next table I get: Estimated demand (after doing some interpolation) = 58.4 GPM
As for the pump head, I am designing for 21 psi at the outlet with the least pressure (highest floor that is)
So my required head would be:
(21psi residual + friction losses + dynamic losses) MINUS elevation head between pump and outlet (pump is placed on the roof next to the roof water tanks)
Thus my pump is selected for: 58.4 GPM @ calculated head as shown above.
Am I doing this correctly? Any corrections/comments are highly appreciated.
Best Regards
I am working on selecting a pressure booster pump for a small residential apartment building. I am estimating my peak cold water demand based in the Water Supply Fixture Units, from the American Society of Plumbing Engineering Design Handbook Vol2, Tables 5-18 & 5-19. I'm using the values for combined the hot & cold water because cold water will be fed into standalone water heaters in each apartment, so the hot water demand is ultimately cold water demand. (hope that doesn't sound too confusing)
I have 11 identical flats, each has the following water demand outlets:
2 water closets: 2 x 2.2 = 4.4 WSFU
2 Wash Basins: 2 x 3 = 6.0 WSFU
1 Bathtub: 1.4 WSFU
2 Hand Bidet: 2 x 1 = 2 WSFU (Not in the table, estimated)
1 Kitchen Sink: 1.4 WSFU
Total for 1 apartment = 15.2 WSFU
Total for building = 15.2 x 11 = 167.2 WSFU
From the next table I get: Estimated demand (after doing some interpolation) = 58.4 GPM
As for the pump head, I am designing for 21 psi at the outlet with the least pressure (highest floor that is)
So my required head would be:
(21psi residual + friction losses + dynamic losses) MINUS elevation head between pump and outlet (pump is placed on the roof next to the roof water tanks)
Thus my pump is selected for: 58.4 GPM @ calculated head as shown above.
Am I doing this correctly? Any corrections/comments are highly appreciated.