I had a "seasoned" tradesman in the HVAC industry tell me that over-pumping a coil gives you less heat transfer because the water delta-T is lower. I didn't want to challenge him on the spot because I'm not positive, but that seems wrong to me. Yes it is true that the water delta-T is less, but the increased flow will ultimately result in more heat transfer, correct?
For example, let's say we have a coil passing so many CFM of air and 100 GPM of 180 deg EWT and 160 deg LWT water. Now, keeping the same coil, same EAT, and same EWT, let's increase the flow to 150 GPM. The water delta-T will be less, but when you convert GPM and Delta-T to MBH, it should be more, correct? Air the Leaving air temp should be hotter, correct?
Going to the extreme, if we have a constant temperature coil of 180 deg because we have an "infinite" flow, my air will see more coil surface area of 180 deg. Compare that to a coil that in 160 deg on one side and 180 deg on the other side and it seems obvious.
Am I missing something here, or did that "seasoned" guy make a false statement?
For example, let's say we have a coil passing so many CFM of air and 100 GPM of 180 deg EWT and 160 deg LWT water. Now, keeping the same coil, same EAT, and same EWT, let's increase the flow to 150 GPM. The water delta-T will be less, but when you convert GPM and Delta-T to MBH, it should be more, correct? Air the Leaving air temp should be hotter, correct?
Going to the extreme, if we have a constant temperature coil of 180 deg because we have an "infinite" flow, my air will see more coil surface area of 180 deg. Compare that to a coil that in 160 deg on one side and 180 deg on the other side and it seems obvious.
Am I missing something here, or did that "seasoned" guy make a false statement?