Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Limits for repetitive induction motor DOL starting

Motor Starting

Limits for repetitive induction motor DOL starting

by  electricpete  Posted    (Edited  )
The following link gives NEMA MG-10 recommendations regarding maximum starting frequency and required off time between starts as a function of motor horsepower, speed, and load inertia which apply for NEMA frame motors (typically 250hp or less). These are repetitive starting limits targeted toward chronic long-term use.

https://www.efficientplantmag.com/2015/05/safe-starting-of-motors-check-for-temperature-increase/

These limits do not extend to the range of large motors. For those motors, additional info is needed from OEM to evaluate repetitive starting duty.

There may be other less restrictive limits for acute repetitive starting such as 2 successive starts allowed if motor was initially cold as allowed per NEMA. Long term repetitive starting are different than infrequent acute limits, however applying the limits / times for long term to evaluate acute duty would be conservative and may be the best option when there are no other allowances accessible.
Register to rate this FAQ  : BAD 1 2 3 4 5 6 7 8 9 10 GOOD
Please Note: 1 is Bad, 10 is Good :-)

Part and Inventory Search