.
Here are the governing relationships for the makeup flow rate, the evaporation and windage losses, the draw-off rate, and the concentration cycles in an evaporative cooling tower system:
M = Make-up water in gal/min
C = Circulating water in gal/min
D = Draw-off water in gal/min
E = Evaporated water in gal/min
W = Windage loss of water in gal/min
X = Concentration in ppmw (of any completely soluble salts à usually chlorides)
X[sub]M[/sub] = Concentration of chlorides in make-up water (M), in ppmw
X[sub]C[/sub] = Concentration of chlorides in circulating water (C), in ppmw
Cycles = Cycles of concentration = X[sub]C[/sub] / X[sub]M[/sub]
ppmw = parts per million by weight
A water balance around the entire system is:
M = E + D + W
Since the evaporated water (E) has no salts, a chloride balance around the system is:
M (X[sub]M[/sub]) = D (X[sub]C[/sub]) + W (X[sub]C[/sub]) = X[sub]C[/sub] (D + W)
and, therefore:
X[sub]C[/sub] / X[sub]M[/sub] = Cycles = M / (D + W) = M / (M û E) = 1 + {E / (D + W)}
From a simplified heat balance around the cooling tower:
where:
H[sub]V[/sub] = latent heat of vaporization of water = ca. 1,000 Btu/pound
[Δ]T = water temperature difference from tower top to tower bottom, in [°]F
c[sub]p[/sub] = specific heat of water = 1 Btu/pound/[°]F
Windage losses (W), in the absence of manufacturer's data, may be assumed to be:
W = 0.3 to 1.0 percent of C for a natural draft cooling tower
W = 0.1 to 0.3 percent of C for an induced draft cooling tower
W = about 0.01 percent of C if the cooling tower has windage drift eliminators
Concentration cycles in petroleum refinery cooling towers usually range from 3 to 7. In some large power plants, the cooling tower concentration cycles may be much higher.
(Note: Draw-off and blowdown are synonymous. Windage and drift are also synonymous.)
In SI metric units:
M = Make-up water in m[sup]3[/sup]/hr
C = Circulating water in m[sup]3[/sup]/hr
D = Draw-off water in m[sup]3[/sup]/hr
E = Evaporated water in m[sup]3[/sup]/hr
W = Windage loss of water in m[sup]3[/sup]/hr
X = Concentration in ppmw (of any completely soluble salts à usually chlorides)
X[sub]M[/sub] = Concentration of chlorides in make-up water (M), in ppmw
X[sub]C[/sub] = Concentration of chlorides in circulating water (C), in ppmw
Cycles = Cycles of concentration = X[sub]C[/sub] / X[sub]M[/sub]
ppmw = parts per million by weight
A water balance around the entire system is:
M = E + D + W
Since the evaporated water (E) has no salts, a chloride balance around the system is:
M (X[sub]M[/sub]) = D (X[sub]C[/sub]) + W (X[sub]C[/sub]) = X[sub]C[/sub] (D + W)
and, therefore:
X[sub]C[/sub] / X[sub]M[/sub] = Cycles = M / (D + W) = M / (M û E) = 1 + {E / (D + W)}
From a simplified heat balance around the cooling tower:
where:
H[sub]V[/sub] = latent heat of vaporization of water = ca. 2260 kJ / kg
[Δ]T = water temperature difference from tower top to tower bottom, in [°]C
c[sub]p[/sub] = specific heat of water = 4.184 kJ / kg / [°]C
Windage losses (W), in the absence of manufacturer's data, may be assumed to be:
W = 0.3 to 1.0 percent of C for a natural draft cooling tower
W = 0.1 to 0.3 percent of C for an induced draft cooling tower
W = about 0.01 percent or less of C if the cooling tower has windage drift eliminators
Concentration cycles in petroleum refinery cooling towers usually range from 3 to 7. In some large power plants, the cooling tower concentration cycles may be much higher.
(Note: Draw-off and blowdown are synonymous. Windage and drift are also synonymous.)