    Dear kslee1000, I agree, my point is that we cann't use gage more than 4 1/2" for web 3/16" [ because max. spacing should be 3/16" x 24 = 4.5" and in that case we should use narrow gage 4" ( (2)-L 3 1/2x3x5/16 ) ]. Sincerely,
  2. borisng

    BOLTED BEAM TO BEAM ANGLE CONNECTIONS

    Dear StructLin, Sorry, I mean W12x14. Sincerely,
  3. borisng

    BOLTED BEAM TO BEAM ANGLE CONNECTIONS

    Dear StructLin, there is some limitations for max. distance in bolt's (rivet's)group between bolts (rivets)as you know. One of it for web 3/16" thk. is 3/16" x 24 = 4 1/2". Sincerely,
  4. borisng

    BOLTED BEAM TO BEAM ANGLE CONNECTIONS

    Dear NUTTE, What you would do if you need to make built-up beam (girder) with web 3/16" thk. and to make assembly with bolts or rivets? Sincerely,
  5. borisng

    BOLTED BEAM TO BEAM ANGLE CONNECTIONS

    Dear NUTTE, Thank you for your answer. It seems to me all bolts consist of one group of bolts. I suppose that this requirement provides a work of bolts together and reduce deformations in connection - as web as angles. What do you think? Sincerely,
  6. borisng

    BOLTED BEAM TO BEAM ANGLE CONNECTIONS

    Dear Sir/ Madam, We have framing with beams W12x22 and W10x12. The web thk. of both of it 3/16". The same time we use double-angle ( (2)-L 4x3 1/2x5/16 )connections with wide gage 5 1/2". It seems to me we can not do it because max. spacing should be 3/16" x 24 = 4.5" and in that case we...
  7. borisng

    ASD - 6 kips LRFD - 10 kips for stair

    Dear Sir/ Madam, Please, confirm: 1. the spacing shall not exceed 4.5" for web's thk. 3/16" (MC12x10.6) or 2. we should take stringer with thicker web. Sincerely,
  8. borisng

    ASD - 6 kips LRFD - 10 kips for stair

    Dear nutte, thank you for answer! The same time, please, take a look on the comentary for 13-th edition of AISC manual. They are plaeing a game - for next edition they will put it up site doun. Let me ask you about max. spacing for bolts. Some fabricators makes bolted tread connections to the...
  9. borisng

    ASD - 6 kips LRFD - 10 kips for stair

    Dear Sir / Madam, Could you provide any comments about Minimum Strength of Connections according to: - ASD - it should be proportioned to 6 kips and - LRFD - it should be proportioned to 10 kips. How to use these norms for Stairs calculations and especially for: 1. tread's connections to...