Recent content by CanuckPE

  1. CanuckPE

    Signal interference with Tr!mlight system

    Update: Sorry, it's been a while. The contractor returned to install all new "shielded" wire conductors from the controller to the lights. The shielding is essentially tin foil between the outer sheathing and the conductors. The shielding is obviously not grounded in this case. We changed the...
  2. CanuckPE

    Signal interference with Tr!mlight system

    I will confirm the load with the contractor. With the new power source, it should have lots of capacity at 15 amps, and around 110 volts.
  3. CanuckPE

    Signal interference with Tr!mlight system

    Nothing that I'm aware of for cycling on the pattern of the blue streak. Does the wire cover need to be tin foil, or could I use a thin galvanized steel conduit? Would the GS conduit have the same effect as the foil, or does the conduit need to be aluminum? I haven't seen any ham radio...
  4. CanuckPE

    Signal interference with Tr!mlight system

    The power was from the same source, which moves the needle away from the power source. I've plugged the system into a different power source/breaker from the panel. It's a 15 amp service with a single 14-2 conductor and one plug on it. The previous power source was a highly loaded circuit that...
  5. CanuckPE

    Signal interference with Tr!mlight system

    There is a manufacturer's site. Tr!mlight is spelled with an "i". I'm using a pseudo name to avoid liability. The contractor is a one-person operation. He's been in touch with the technical support folks from the manufacturer.
  6. CanuckPE

    Signal interference with Tr!mlight system

    Thank you waross. I'll give this a shot if the alternative power source doesn't tune up the problem. Will post again in the morning.
  7. CanuckPE

    Signal interference with Tr!mlight system

    This is a proprietary system, and I don't see it sold online. Only "professional" installers that are associated with the vendor may sell and install. That said, the wires and lights look like the most cheaply produced garbage from China that you would find at Princess Auto (I'm in Western...
  8. CanuckPE

    Signal interference with Tr!mlight system

    Thank you for you comments, RedSnake. I was thinking the disturbance, if caused by the garage lights or ballasts, would be proximity-based if the disturbance is active only when the wires go through the attic space. The disturbance occurs when the garage lights are off. The contractor...
  9. CanuckPE

    Signal interference with Tr!mlight system

    I will try a fresh power source. I'll try something with a short distance from the panel and a big extension cord. That will be a lot less work than shielding the wires. Thank you!
  10. CanuckPE

    Signal interference with Tr!mlight system

    I've had a contractor at my house (single family) for several days. He's been endeavoring to figure out what's causing a signal interference issue with my Tr!mlight system that he installed. For days I suggested he, "figure it out for himself," but his presence at my the house is starting to...
  11. CanuckPE

    Hydraulic Area - Converting a box culvert to a series of circular culverts

    I'm not much of a hydraulics guy, but I do have a mech degree and I practice a bit in piping. A client asked if we could provide services/plans to convert a box culvert (old, wooden, bad condition during inspection) to a series of circular CMP culverts. In lieu of a more complete study of the...
  12. CanuckPE

    Geotechnical Modeling of Potash/Muck Backfill

    I've been tasked with estimating the remaining time to required repairs for a tubular corrugated steel structure with a potash/mining muck backfill and traffic over the backfill. The tube was placed in a mining drift and the perpendicular drift above has the traffic. The side of the tubes are...
  13. CanuckPE

    Frp partial material resistance factor in Canada

    Thank you KootK! Much appreciated.
  14. CanuckPE

    Material Selection for Sodium Hydroxide and Hydrochloric Acid

    Thanks for your response EdStainless I utilized the nickel institute documents and website for my cursory research. I can confirm MTI-global requires a membership to view their documents. If they have anything definitive on caustic/acid cocktail and you're willing to share, please do so...
  15. CanuckPE

    Material Selection for Sodium Hydroxide and Hydrochloric Acid

    I've been asked to select materials in the bid stage for a chemical processing facility. We do tanks, but typically the material selection for our tanks is one step up the engineering chain. I've performed some cursory research, and I have some undergraduate-level training in material...