Hello everybody.
I’m from Portugal and we have many Electrical Engineering MSc degrees with different branches, like energy, telecommunications, automation and electronics.
In your own countries, can an Electrical Engineering MSc in branches, other than energy, be responsible for the project...
Good evening everybody.
I’m an electrical engineer and I have a safety question regarding a safety butterfly valve that closes automatically after an excess flow detection.
I’m familiar with these systems and, if the valve does close, I think it’s mandatory that the reset is always a manual...
Hello everybody.
I am looking for a lighting calculation software for a road tunnel project.
I have come across Relux Desktop which is free.
There is a Tunnel lighting add-on available to buy.
But it seems it’s included in the free downloadable Relux Desktop package.
Has anybody tried the...
Good afternoon everybody.
I am involved in a project and I want to calculate the fault currents on several locations to validate the short-circuit power needed for each panel and the upstream trip switches nominal currents and its types A, B, C or D.
I use the impedances method and determine...
Hello waross,
The inertia constants were calculated. When I refer thermal power plants I mean fuel or natural gas prime-movers.
Based on bacon4life infos, I think I´ve made a step forward on the subject. One should consider the Kinetic Energy which is H x S.
A 2s inertia constant, 10MVA...
Bacon4life let me clarify my concern.
I’m not focusing only on inertial response. I work for the power generation department.
We have old 14 MVA fuel generators, with mechanic speed governors, with 2 s H inertia constants.
Then we have modern 21 MVA natural gas generators, with digital speed...
Good morning everybody.
Some grid stability studies neglect the demand side inertial contribution. Only compute the synchronous generators inertial contribution.
Other studies refer that, on the demand side, there are synchronous motors that must be considered.
The majority of electrical...
I work for the utility so the difference costs of fuel and natural gas is not really an issue.
Of course we want to stop the fuel thermal power plants in due time for ecological reasons.
We don’t have what we call an isochronous machine. All work on 3% droop. That’s the primary control. Then...
Good afternoon Waross.
Thanks for your quick reply.
I live in Madeira island and our isolated grid is only 120 MW worth, isolated.
We have natural gas and fuel thermal power plants. Also, hydro, windpower and photovoltaic power plants.
The natural gas power plant is equipped with three 21 MVA...
Good afternoon
Suppose I have two synchronous generators. One rated 10 MVA with H=4s and the other 20 MVA with H=2s.
I understand that the SIRs of the generators don’t depend on their operating point.
But if both are working at, let’s say, 5 MVA, and there’s an outage of another generator in...
Good night experts.
I work for the utility in Madeira island. Our grid is small and not connected to Portugal mainland.
I want to validate our RoCoF figure. I have calculated all the synchronous generators (Si) inertia constants (Hi).
I´ve used Hi= (J*Wi^2)/(0.5*Si).
I´ve read somewhere...
Good evening everybody.
Can a diesel generator, connected to the grid, absorb reactive power while producing active power?
A small grid, with underground power cables and frequency converters everywhere, can have a surplus of capacitive reactive power. That raises the grid voltage, mainly...
Hello electricuwe
You are correct. IT system is only for the pumps.
I understand the emergency equipments must comply with IT requirements. For example, if they are single phase, they must be suitable to a 400VAC voltage between phase and earth. The pumps will be delta connected but the...
This is what I meant:
https://files.engineering.com/getfile.aspx?folder=111e953e-d217-43be-991e-61de2b75aaae&file=14D65E04-7406-4865-BF49-0F4BEB2904F8.jpeg
Hello everybody.
I’m planning an IT earthing system to feed some emergency pumps within an existing building.
The existing electrical installation is on a TT scheme.
There will be, of course, a specific LV/LV transformer with a Permanent insulation monitor.
I will install an equipotential...