  1. carlossteiner

    Cross Bonding Surge Arrestor

    The Images you post are from a TYCO ELECTRONICS Presentation. Well Thanks every body for your help!
  2. carlossteiner

    Cross Bonding Surge Arrestor

    5.7 Cable sheath protection of high-voltage cables For thermal reasons and to reduce losses along a cable, the cable sheath or screen of highvoltage single-core cables is mostly earthed at one end only. The unearthed end must then be protected with arresters against transient overvoltages. The...
  3. carlossteiner

    Cross Bonding Surge Arrestor

    Magoo2, What cuky2000 is traing to explain is ok, but I think it is for the selection of surge arresters. I am attaching a a file from my librarie. About cross bonding, what you are writting is right, but usualy in those points the cable sheath is grounded through a surge arrester. It is this...
  4. carlossteiner

    Cross Bonding Surge Arrestor

    I would like to know if there is a methot to determinate the kV of a cross bonding surge arrestor. The standard method as used by NGTS in the UK is to select an arrester with a Ur of 1kV per 10kA RMS through fault current at the point of installation. So if the fault level is 40kA, then the...