Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by crshears

  1. crshears

    To replace faulty power alternator with a smaller unit

    Operational and thermodynamic analysis would answer that one; I recall working with an operating engineer who would lower the boiler pressure set point when at reduced / minimum load overnight, instead of just throttling down. Interestingly [ at least to me! ], for the six plus years I worked...
  2. crshears

    Get the required proprties from the property window from the bundle segment in catia v5 using vba

    I could help if I understood what you're talking about . . . but I don't, plus I am not doing your work for you. I suggest you peruse the list of forums and find the one which best covers your topic of interest.
  3. crshears

    Get the required proprties from the property window from the bundle segment in catia v5 using vba

    wrong forum for your question - please re-post correctly and delete this one
  4. crshears

    Question about LTC Transformers

    The Technical Interface Requirements or equivalent of the Authority Having Jurisdiction [AHJ] will largely determine the answer to your question.
  5. crshears

    KW, KVA, KVAR relationship

    Hi JC, The theory that follows holds up in real life. The power triangle shows [1] real power, where voltage and current are in phase; the product of volts x amps equals watts, 746 of which make one horsepower, which involves doing actual work, which requires energy expenditure, in your case...
  6. crshears

    KW, KVA, KVAR relationship

    Just to help you double check your math, this page https://www.allaboutcircuits.com/textbook/alternating-current/chpt-11/true-reactive-and-apparent-power/ gives a diagrammatic tutorial on real, apparent and reactive power. Like Bill [waross] said, power factor is determined by the load, not the...
  7. crshears

    KW, KVA, KVAR relationship

    Welcome to the forums, JC. My first questions are, "Measured where? And how have you determined PF is leading?" Since you just joined and your profile doesn't tell us much about you, my response may be a bit pedantic, but I've learned to live with that. As a retired power system / grid...
  8. crshears

    TC bolt

    wrong forum
  9. crshears

    power factor issue

    Hello zoo, waross is correct; I agree more with his second recommendation, viz., you should find a local expert in power factor penalties. My reference was to a power factor correction unit that connects at the point of common coupling, meaning where your electrical services and your power...
  10. crshears

    power factor issue

    Hmm, have I not seen threads in these fora relating to commercially available small scale power factor correction units for use at Point Of Common Coupling [ POCC ] ? You might want to do a search . . .
  11. crshears

    Paralleling dissimilar Generators

    More problems, or more generators? :cool:
  12. crshears

    Siphon

    Why not? If lower valve is closed and aspirator draws water up from the upper reservoir, will it not spill over the saddle of the apogee and prime the downstream side as well? Or am I missing something?
  13. crshears

    Siphon

    If a valve is placed at the outlet and closed during priming, cannot an aspirator be used at the top of the siphon to extract the contained air? This would obviate the need for a foot valve at the inlet.
  14. crshears

    Electric Boiler Question

    "Unfired" perhaps, but not without energy input; ability to liberate steam in such volumes as needed to preclude boiler or system over-pressurization is still very much in play.

Part and Inventory Search