Interesting question OP and thanks for the well written post with accompanying sketches! A couple comments/questions that I have:
1) What does the base of the pole look like close up? If it was installed plumb and rotated afterwards, there may be signs of cracking in the pavement surrounding...
I don't know much about underpinning but the one residential project I was involved in, a similar detail was used (without the the stem extending above existing footing). The underpinning designer specified dowels drilled up into the bottom of exiting footing. It might have been less than 12...
For sliding issues, do you have a slab on grade to depend on? If so, I would include all the friction resisting force between the slab on grade and soil, in addition to the total weight of your building too. Like others have mentioned you should also include the sliding resistance provided by...
What is the maximum width of the RTU on plan? If it is less than 15 feet then you don't need to consider any additional snow drift.
EcoGen Consultants LLC
Structural Engineers
ecogenconsultants.com
I've done a couple of these. Can't remember what our fee ranges were in the past. Keep in mind, it's the PEMB designer's responsibility to make sure they give you the correct gravity and lateral load reactions at each column location. Using those reactions it'll be pretty straightforward design...
We have specified this in the past but you will need a way for the horizontal shear to get into the slab from the column. You can do this by specifying "hairpin" tie bars that wrap around the concrete pier base below the column and each leg of the hairpin extends at 45 degrees into the SOG. What...
In all honesty, I'm not familiar with swell tests and how that affects your foundation calculations. But regardless, shouldn't a geotechnical engineer/report determine what exact soil improvement or modification is required to obtain the required 2,000 psf? If a geotech report/testing is an...
What @Enable said. Nothing of what you have presented so far warrants demolition.
I'll also add that you shouldn't be sealing the crack from below since it can trap any moisture in the slab if it does eventually get in there. What does the top surface of the slab look like? If you can see the...
I agree with all of the above. We shouldn't be fixing Contractor issues for free regardless of how much fee or how many hours we have left in the job. We should make it clear to our clients in writing but also in person, that any deviation from details, construction issues caused by the...
First I would verify with the owner that the foundation wall is actually concrete and not CMU block especially since you're saying it's 8 inches thick. Don't take their word for it, visit the site yourself or ask for clear photos showing exposed concrete aggregate faces.
If it's CMU block...
That didn't seem right to me at first so I ran it in ENERCALC and got about the same width (9 feet) to meet 1.5 F.S. for sliding. Another option would be to use a key. Even then to get to 1.5 F.S. you would need about a 24 inch deep x 12 inch wide key which gets you to about a 5 foot wide...
1) The length of the wall is 22 inches or you're saying the wall is 22 inches thick? That would be way too thick of a multi whythe wall unless it's hollow with cavities between each wythe.
2) The brick wall bears on a brick footing? So basically the same wall just continues straight downwards...
Can you provide a sketch of it? It's not clear to me what the issue is based on your description.
EcoGen Consultants LLC
Structural Engineers
ecogenconsultants.com
I also think some Contractors ignore some of our repair details too because they don't want to spend the 20 mins figuring each component of the detail out. Using isometric views would be a step in the right direction for some of our very typical repair details and most new construction details...
If you're not responsible for the pier design itself, I would have the Geotech Engineer somehow sign off on the reactions you determine from the structure and grade beam onto the pier.
EcoGen Consultants LLC
Structural Engineers
ecogenconsultants.com