    Roof without flat ceiling - how to resist thrust?

    Run the header long and fasten as many SDWC screws up from the top plate as your heart desires. Depending on the size of the opening and width of the header I have called for straps on the underside of the beam to the bottom chord to resolve the torsion.
  2. Flotsam7018

    interior truss heel sheathing

    I definitely get concerned with adequate rollover restraint and keeping the end vertical plumb in situations like this. So I don’t find it overkill, especially since I’ve seen a lot of truss bracing missed or not installed properly. I have specified truss panels between trusses at an interior...
  3. Flotsam7018

    Double shear plate as a column beam connection

    As in a double shear tab connection? If so, this could work if you need the extra shear plane for the bolts, not seeing any other benefit. This connection is more difficult to erect so I would generally avoid unless the condition is very unique.
  4. Flotsam7018

    Rectangular HSS Column/Round Base Plate Design

    Consider the case with the anchor furthest from the face of the HSS and determine the effective width of the circular plate based on 0.95 of the HSS per AISC DG 1. If you really want to get fancy you could consider prying, though this is typically not done for baseplates and would be less...
  5. Flotsam7018

    Concrete edge breakout for multiple anchors in a single row (drag load)

    It's basing the group capacity on the rear anchor only, once the shear failure plane is developed there the rest of your anchors will just go along for the ride. I've only ever had situations like this is new construction and have always use shear reinforcement.
  6. Flotsam7018

    Ordinary Moment Frame Connection Upgrade

    Yes, adding stiffeners in the correct locations will result in additional yield lines in the end plate. Have a look at AISC Design Guide 39, the basis of which is yield line analysis but they provide simplified equations, one of which likely fits your scenario.
  7. Flotsam7018

    Steel Beam to Steel Beam at Steel Column Residential Connection

    My only suggestion would be to make it a bolted cap plate connection.
  8. Flotsam7018

    LVL End Nailing

    Most of us rely on end nails for some things such as typical stud to wall plate, header to king stud, etc. But yeah, I don't rely on them for gravity loads.
  9. Flotsam7018

    Looking for some ideas on a unconventional connection design

    Firstly, I’d try to locate the bolts in the splice connection as close as possible to the centroid of the angle/weld group to avoid additional moment on the bolt group. This is likely something mirrored from what you show. Then I’m with KootK, scrap the stiffeners and just go with a thicker...
  10. Flotsam7018

    Lateral Design for Open Porches

    As with any residential engineering, it is a fine balancing act of practicality, common sense and true engineering rigor. However, I do think it is our job to provide a complete load path - otherwise why the heck is anyone even paying us, they mind as well just have the designer/builder figure...
  11. Flotsam7018

    I need a sanity check - Drilled Pier depth determination in Lpile

    Agreed that your deflection tolerance seems very conservative. In my experience the top deflection was the primary serviceability criteria and was typically a ratio of the depth or a maximum magnitude such as 1", whichever is less.
  12. Flotsam7018

    Lateral Design for Open Porches

    Yeah, I don't know about relying on just the valley sleeper for wind perpendicular to the ridge. I typically use the beam below the rafters at the eave as the chords and tie in from there using your favorite deck tie product. Again, this gets more complicated if you're coming in away from the...
  13. Flotsam7018

    Lateral Design for Open Porches

    I almost always treat it like a deck and tie the chords into the main diaphragm as long as it meets the SDPWS requirements, which this does. Is everyone analyzing all the transfer diaphragms for lateral deck ties? My guess is not. Sometimes tying back can be goofy depending on the demand and...
  14. Flotsam7018

    Working On House with Modified Trusses, yes or no?

    If it didn't feel right, passing on the job is probably the best call for you personally. However, why did you feel the trusses need to be analyzed - simply because it's non standard construction or were there signs of deficiency observed? If it's been performing adequately for some time, I...
  15. Flotsam7018

    Bolts and T-Stubs and Prying, Oh My!

    Is it possible this is due to fabrication and fit up issues rather than flexural yielding of the plate? Only one side of the connection appears to have rotated. Either way, if the numbers show that the first hinge at the HSS yield under dead load only I would certainly call for remediation. A...