Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SDETERS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by GT-EGR

  1. GT-EGR

    dP Sensor Location & PICV's

    The 2/3 rule always seemed like a vague way for someone to easily call out a sensor spot without putting too much thought into it, mostly because it can be complex in theory but then you can install it in different spots and still get it to work out. The PICV will handle the over pressure...
  2. GT-EGR

    Medium pressure ductwork

    Still would be done the same way, using a damper or a VAV box which is basically an automatic damper to drop the pressure and regulate flow quantity before it is discharged into the space. Or you said valve which in a critical space is a particular type of Venturi which again just reduces the...
  3. GT-EGR

    CO2 Air to Water Heat Pump w Solar Pre-heat

    The way this information is being presented I think is the confusing part. Yes as the entering temperature gets higher, you get less heat pump heating output aka lower efficiency. This is just due to the ability to transfer heat from the refrigeration cycle if the water starts off...
  4. GT-EGR

    How well do cooling only VAV's with perimeter heat work?

    My experience is that the interior office type spaces you can usually get away with it since the minimums are so low. But the conference room high occupancy high minimum airflow spaces are the issue. You can resolve those by using minimum ventilation reset strategies which is somewhat code...
  5. GT-EGR

    Exhaust for Cannabis Cultivation

    Code doesn’t specifically require exhaust for cannabis cultivation itself. But some of the supporting elements of the operation like CO2 use and making sure you have protections and purge capabilities during accidental release would end up indirectly leading you to exhausting certain areas that...
  6. GT-EGR

    How much pressure is required by an exhaust fan when it exhausts straight up?

    Calculating on the exhaust discharge side is barely any different than on the suction inlet side You do your normal calculation and fitting loss lookups based on your exhaust airflow, and the duct size and velocity the air is traveling through. You also may have to account for velocity...
  7. GT-EGR

    Vav with FCU

    I would guess that the FCU is recirculating in the space so provides heating and cooling but no ventilation. Then the VAV provides ventilation air to the space, but not at a quantity near enough to cool or heat the space. I also see this a lot in labs with high cooling loads (FCU sized for it)...
  8. GT-EGR

    DIVERSITY FACTOR - HEAD PUMP - CHILLED WATER SYSTEM

    Here’s an example of a simple approach that is slightly conservative and doesn’t take much any extra effort. Let’s say you have 4 coils that each need 60 GPM, but your max load is 200 GPM. Identify your critical run, and do the pressure loss calc of the most remote branch at 60 GPM, when it...
  9. GT-EGR

    Reset pressure setpoint method and primary pump variable speed

    It’s very similar to the traditional way where you picked a DP reading and target setpoint somewhere remote in the system. Major install difference is you need feedback on the valve positions to your controller. Otherwise pick and design to a starting DP setpoint as you always would have...
  10. GT-EGR

    Reset pressure setpoint method and primary pump variable speed

    Secondary loop differential pressure reset algorithm generally takes feedback of some or all of the critical chilled water consumers in the loop, decides if a high quantity or all of the valves are in need of that much flow/pressure, and then resets the DP setpoint up or down in response to...
  11. GT-EGR

    Hydronic pressure loss mystery

    Twice in the past year we lost boiler pressure to the point of tripping the low water cut off devices - have you ruled out that the low after cutoff is functioning properly? I assume this 6th floor boiler is above a significant volume of the building loops it feeds correct? You’d have to...
  12. GT-EGR

    Building Pressurization

    A value like that is useful to plan some extra outside air capacity. But it really all depends on what your control method is, how tall your building is, and how extreme your summer and winter temperatures are. I’ve never seen an all encompassing approach because building pressure targets are...
  13. GT-EGR

    Ethylene or Propylene glycol for HVAC system

    See attached, just came across this brief summary in ASHRAE journal last November article about runaround glycol heat recovery loops. https://files.engineering.com/getfile.aspx?folder=f9c004f3-3101-4b8f-9745-92d46302e027&file=BC1208C7-1BDC-4718-BBF3-92F500DC7DD5.jpeg
  14. GT-EGR

    Ethylene or Propylene glycol for HVAC system

    I trace back the anti-EG sentiment to the link below. Heavily regulated and compliant Facilties see EG as one more potential item to track. PG doesn’t have anything out there like this so it is casually regarded at times as the safe alternative. https://rcrapublic.epa.gov/files/14163.pdf
  15. GT-EGR

    Walk-in Cooler/Freezer Demo

    Only thing I’d add to these answers is if you don’t remove the outdoor unit at least label it as abandoned and what it used to do. In a building with a lot of condensers this can sometimes be a big help to us poor engineers trying to trace out tiny refrigerant piping.