Recent content by hasanhadi

  1. hasanhadi

    open delta transformer

    thank yor dear sorry dear ratio for transformer (33kv/1.73)/110/1.73
  2. hasanhadi

    VCB vd4

    thank you.http://files.engineering.com/getfile.aspx?folder=adb1d867-34b9-42e6-8ff7-655b8b279c68&file=2.jpg
  3. hasanhadi

    VCB vd4

    Mr.smallgreek today measuring voltage by using anloge meter but reading not change after that connect light no change in reading i mean Vn=400 v VL-L=710v and connect resistance also no change in reading Mr will drawing state in the file attachment
  4. hasanhadi

    VCB vd4

    sir iam sorry but cannot connect resistance why? because the device relay is reading 400v voltage to neutral and 700 volt phase-to-phase this voltage is real in busbar now can be obtain zero voltage by drawing breaker in test position but only i need know reason for why voltage 700 in basbar...
  5. hasanhadi

    transformer three winding

    hi we have transformer three winding 132kv/33kv/6.6kv and power 63MVA now how dividing load crossing winding i mean when load from side 6.6kv this effect to side 33kv or only loading for 132kv onther words when loading to side 6.6kv is effect to 132kv(primary) or effect too to 33kv
  6. hasanhadi

    earthing system

    hi how calculated rated for time example if NGR=38 OHM for 10 sec but i need calculated for value NGR if time 1min or 10 min also if rated for transformer 100kvA FOR 10 SEC WHAT RATED for 1 min i need how calculated or i need equation
  7. hasanhadi

    VCB vd4

    thank you master look when breaker in service position and open and incomer is live( I mean 33kv is found) Problem the bus is reading vn=400v or VL-L=700v i mean founding VT capacity 100VA but when loading by big transformer the voltage will zero now VCB test by car test but the car no...
  8. hasanhadi

    open delta transformer

    thanks sir but can you help me for calculation damping resistance?
  9. hasanhadi

    VCB vd4

    Mr. smallgreek what you mean please i need more information you mean distance between fixed contact and verable contact is not enough to reducing capacitive how solution this problem
  10. hasanhadi

    Varlogic NR6 -N12

    i know but Varlogic NR6 -N12 cannot reading true power i mean source voltage 6600 but voltage in device 110v how matching between this voltage to obtain true reading in medium voltage in maunal said In HV applications the power values displayed in Measurement Menu represent only the...
  11. hasanhadi

    open delta transformer

    hi we have vt transformer Y/y/d 33kv/110/110 now d is connected open to detection earth fault true? the end for open delta is connected to damping resistance now 1- Why take advantage for using damping resistance? 2- how calculated value damping resistance? 3-when not using damping...
  12. hasanhadi

    earthing system

    hi how calculated rated power for 1- zagzag transformer with 10sec,30sec,1min,10min 2- NGR with 10sec,30sec,1min,10min 3- reactance with 10sec,30sec,1min,10min 4-star-delta closed with 10sec,30sec,1min,10min i need equation for calculated this informaton is very importment please and thanks
  13. hasanhadi

    Varlogic NR6 -N12

    what is mean set the CT ratio to percentage scale? also when change to the ct ratio to percentage scale on effect to power factor i need example please how matching if I=400A and vt=110 volt,pf=0.9 but voltage source 6600V now power=1.73x110x400=76.2kw but true value=4.57MW
  14. hasanhadi

    Varlogic NR6 -N12

    what is mean set the CT ratio to percentage scale?
  15. hasanhadi

    VCB vd4

    hi We have in AIS ABB substation breaker 33kv (VD4) VCB made in ABB china But when breaker in service position and open and incomer is live( I mean 33kv is found) Problem the bus is reading vn=400v or VL-L=700v why? Must be reading zero because breaker off Now if breaker is drawing to...