Good morning,
I have a query about public address system cabling. What is the maximum distance that a loudspeaker can be placed from the control panel using 100v speaker cabling?
Thanks
Thanks for this. Am I correct that only one transformer/generator can be connected to the NER at the one time and this is achieved through disconnect switches and logic.
Thanks
Hello,
I have a question regarding the use of one Neutral Earthing Resistor per substation for two transformers. Can anyone point me in the direction of websites/ literature that would show the operational philosophy of this set up compared to one neutral earthing resistor per transformer...
Hello,
With regards to 3 core 11kV cables run in parallel on a ladder that need to be jointed. is there a standard to say what the spacing should be between joints ?
Thank you
Hi,
I have a query in relation to MV fault levels for an 11kv switch board. How is the fault rating (x kA for x seconds) calculated from the following information:
3 phase fault
Line to ground fault
Line to line fault
Line to line to found fault.
For each of these scenarios we have
I”k
Ip...
Hello again,
Does anyone know if there is a HD monitor available that can connect to the CCTV network Poe IP switch ( at a secondary location) so the cctv can be viewed at this second location.
Thanks
Hi,
I have a question about POE cctv systems tying into an existing site fibre network. I understand that a POE switch will be required for the cameras and also a Poe extender for camera distances greater than 100m from the switch but does anyone have an example architecture drawing to show how...
Hello,
Is it a requirement to have an earth switch fitted on 11kv fixed pattern switchgear as a contractor is saying an earth switch is only applicable to withdrawable switchgear.
Thank you
Hi,
With regards to bs7671 are there any rules regarding when to install a distribution board?
For example say we have a main switch board that is feeding pieces equipment separately but these pieces of equipment are quite local to each other would it then be better to take one feed from the...
Hi,
With regards to a Siemens DO card which has outputs rated 0.5A@24VDC if we are using these output channels to power 24VDC solenoid valves (0.3W &7w)would these require interposing relays as they are within the limits of the channel?
Thanks
Thanks for the replies. Please see attached data sheet for a lamp which is24vDC. The data sheet has three connections I believe then that a 3 core cable should be provided but if this lamp is 24vdc then I am unsure as to why the earth is needed?
Thanks...