Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by JezNZ

  1. JezNZ

    Earthing/Grounding of Structures beneath Transmission Lines

    Thanks for response, however fyi I found DL 01.04 is much more relevant, specifically section 6.5.1 pretty much covers off the question.
  2. JezNZ

    Incoming device as Disconnector Switch / Isolator

    Since this is LV. Use a load-break isolator, not a disconnector (off-load). There's no real purpose to put circuit breakers on both the supply side and at the incomer of a board unless this something like a rising main configuration, where that incomer will also serve other boards.
  3. JezNZ

    Earthing/Grounding of Structures beneath Transmission Lines

    Unfortunately they tend to put bridges where the road is!
  4. JezNZ

    Earthing/Grounding of Structures beneath Transmission Lines

    Hi, I am looking for advice on the grounding / earthing of structures beneath transmission lines. The scenario is a 220kV line which crosses a waterway, and a temporary steel bridge structure also crossing the waterway is being installed, directly underneath the lines. Does the NESC Handbook...
  5. JezNZ

    Bus Bar Sleeves in Switchgears

    According to IEEE Gold Book - Insulated Bus Bars reduces the likelihood of a bus fault by approximately 90%. Depending on your reliability requirements and cost of outage impacts, that may or may not be a significant figure. On a recent project of 100k/hr plant outage we calculated insulating...
  6. JezNZ

    Explanation for Importance and/or application of the "3*Zero Seq Current" for LG and LLG F

    3 phases, interconnected via various sources or load impedances etc. In an earthed/grounded system, when one phase or multiple phases are faulted to ground, current will 'flow' in all phases in-phase through the system into the fault. This in-phase current is the zero sequence current. In the...
  7. JezNZ

    Modelling an Open Delta (with LV Resistor) Earthing Transformer in ETAP

    Hi All, For the purposes of Fault Analysis, I'm modelling in etap an 11kV industrial system that until recently had embedded generation. The system is earthed via a YNd11 12.1kV / 240V open delta transformer with an LV resistor. I can't find a way to model this in etap directly with the LV...
  8. JezNZ

    Earthing Grid in Power Plant

    Only speaking for my locale, but industry best practice is to always earth/ground metallic substation fences. The rationale being that unbonded fences overtime often being bonded by accident or as part of any upgrades/additions/maintenance, where the earthing/grounding design has not been...
  9. JezNZ

    Ground/Earth Grid Resistance - Intersecting Curves Method

    Hi, I have read up on the use of the intersecting curves method in the Megger earthing guides and some (very old) material by Dr GF Tagg - however the method is not addressed in IEEE80/81. I have also seen a few prior posts in the forum mentioning it. I am curious to understand more detail...
  10. JezNZ

    Watertight Cable Tray - Vertical Run from Pull Box

    You can get specialist sealing products for this kind of application like these: https://www.hauff-technik.de/en/category/cable-entries-1/press-seals-27 Sealing the cables individually with pressure fit seals is the only way you're likely to get a truly watertight penetration in the...
  11. JezNZ

    Grounding and Bonding for 4160V distribution

    1. Start with basic functional earthing. 2. Calculate the fault loop impedances. 3. Calculate your earth fault return current. 4. Determine protection operating time. 5. Determine tolerable safety limits. 6. Determine EPR (Earth Fault Return Current x Earth Grid Impedance). 7. If EPR < Safety...
  12. JezNZ

    Portable Containerised MV 11kV Substations

    Hi, We have a project on-going where we will design-build a containerised portable substation for 11kV vaccuum switchgear. We have built several in the past but not been directly involved in the design. The feedback from speaking to the project managers involved in these works is that the...
  13. JezNZ

    Mitigation of Transferred Potential

    This question has arisen locally in the context of separated HV/LV earth systems in utility system. The standard answers I am aware of consider the relative size of both grids. Since you wish to segregate based on the transferred potential via the earth itself, to achieve what you want, you...
  14. JezNZ

    What kind of fault current calculation is required during ground grid design

    Hi @james64, In general yes. However, it would be remiss to advise you to not perform a specific case analysis as part of your engineering study. To answer to your OP, the kind of simulation you require is power systems analysis, more specifically a short-circuit study. You can reference IEEE...
  15. JezNZ

    Neutral Cable Sizing

    Interesting to hear how the rest of the world does it. Here, in my part of the world, nobody runs reduced size neutrals in LV world anymore. It is technically still allowable, you simply need to show your calculation of the neutral current, but most, if not all, consider it not worth it, given...

Part and Inventory Search