Since this is LV. Use a load-break isolator, not a disconnector (off-load). There's no real purpose to put circuit breakers on both the supply side and at the incomer of a board unless this something like a rising main configuration, where that incomer will also serve other boards.
Hi,
I am looking for advice on the grounding / earthing of structures beneath transmission lines. The scenario is a 220kV line which crosses a waterway, and a temporary steel bridge structure also crossing the waterway is being installed, directly underneath the lines.
Does the NESC Handbook...
According to IEEE Gold Book - Insulated Bus Bars reduces the likelihood of a bus fault by approximately 90%.
Depending on your reliability requirements and cost of outage impacts, that may or may not be a significant figure.
On a recent project of 100k/hr plant outage we calculated insulating...
3 phases, interconnected via various sources or load impedances etc.
In an earthed/grounded system, when one phase or multiple phases are faulted to ground, current will 'flow' in all phases in-phase through the system into the fault. This in-phase current is the zero sequence current. In the...
Hi All,
For the purposes of Fault Analysis, I'm modelling in etap an 11kV industrial system that until recently had embedded generation.
The system is earthed via a YNd11 12.1kV / 240V open delta transformer with an LV resistor.
I can't find a way to model this in etap directly with the LV...
Only speaking for my locale, but industry best practice is to always earth/ground metallic substation fences.
The rationale being that unbonded fences overtime often being bonded by accident or as part of any upgrades/additions/maintenance, where the earthing/grounding design has not been...
Hi,
I have read up on the use of the intersecting curves method in the Megger earthing guides and some (very old) material by Dr GF Tagg - however the method is not addressed in IEEE80/81. I have also seen a few prior posts in the forum mentioning it.
I am curious to understand more detail...
You can get specialist sealing products for this kind of application like these: https://www.hauff-technik.de/en/category/cable-entries-1/press-seals-27
Sealing the cables individually with pressure fit seals is the only way you're likely to get a truly watertight penetration in the...
Hi,
We have a project on-going where we will design-build a containerised portable substation for 11kV vaccuum switchgear. We have built several in the past but not been directly involved in the design.
The feedback from speaking to the project managers involved in these works is that the...
This question has arisen locally in the context of separated HV/LV earth systems in utility system. The standard answers I am aware of consider the relative size of both grids.
Since you wish to segregate based on the transferred potential via the earth itself, to achieve what you want, you...
Hi @james64,
In general yes. However, it would be remiss to advise you to not perform a specific case analysis as part of your engineering study.
To answer to your OP, the kind of simulation you require is power systems analysis, more specifically a short-circuit study. You can reference IEEE...
Interesting to hear how the rest of the world does it.