Recent content by mirilovic

  1. mirilovic

    Trip coil supervision

    Siemens 7PA30, three phase and single phase trip circuit supervision. Go to: 7PA30
  2. mirilovic

    Ungrounded power TR in grounded network

    If i got this clear. Ground fault on one phase couses overvoltages in other two phases and in isolated star point. So I need higher insulation level on TR and on switchgear?
  3. mirilovic

    Ungrounded power TR in grounded network

    Our contractor wants to install power transformer 110/20/6kV, Y,yn9,d11 in a substation. Primary (110kV) wounding of TR is not grounded. 110kV network is directly grounded. Whats are the consequncies of connecting ungrouded primary in grounded network?
  4. mirilovic

    Voltage spikes experienced with a vacuum bottle breaker

    So, what is criterion for use of surge arresters? When they are needed? Do I have to place them every time when feeding motor/dry type transformer?
  5. mirilovic

    CT grounding

    After reading this thread thread240-191665 and this article: http://www.netaworld.org/files/ItemFileA877.pdf, I need to ask one question to get clear something to myself. Article mentioned above, recomends grounding of CT's in protective relay house. I also found same recomendation in some...