Maybe this will help: IEEE Std C62.22TM-2009
Mike
PS Found this paper as well: https://www.sciencedirect.com/science/article/pii/S0378779621005642#:~:text=Line%20surge%20arresters%20are%20installed,to%20a%20poor%20soil%20conductivity.
Assuming you have a MV or HV circuit breaker w/ no "brains", the relay is the brains. So, there will be a slight delay between relay sensing, and the relay issuing a trip command. So it would actually be longer than 2 sec, unless you included the opening time of the breaker.
Mike
There are usually interlocks between a VFD, load side disconnect and the VFD itself (I've never used a starter on the load side of a VFD, but have installed disconnects on the load side of a VFD for local isolation). Drives don't like switching actions on the load side of their terminals while a...
Consider the withstand time of the resistor. A 400A resistor is pretty common, having a 10 second withstand. Extended time ratings means more $$$.
Mike
I use this:
https://www.mitchellinstrument.com/hd-electric-hva-2000-high-voltage-digital-ammeter-up-to-500kv.html?gad_source=1&gclid=EAIaIQobChMI5ZvQ8uesigMVuiytBh3zcxGFEAQYASABEgJz0fD_BwE
Mike
I would just add to dpc's commentary: close-coupled switchgear, i.e. perhaps a power style transformer that is a few feet away from a switchgear lineup, will likely have a SLG fault current (3*Io) greater than the 3PH fault current. As dpc addresses above, this is cause for concern.
Mike
Right or wrong...I used the following:
<5% VTHD
<33% ITHD
Anything above those #'s, I would look into filtering if operational/equipment issues were noticed, etc. I hadn't experienced any operational down-sides to those #'s, but your mileage may vary depending on your installation.
Mike
If I'm not mistaken, if a UPS fails, it will want to transfer from the inverter/rectifier to its static bypass. Maybe this is why the time delay on your UV release didn't work.
Mike