Maybe this will help: IEEE Std C62.22TM-2009
Mike
PS Found this paper as well: https://www.sciencedirect.com/science/article/pii/S0378779621005642#:~:text=Line%20surge%20arresters%20are%20installed,to%20a%20poor%20soil%20conductivity.
Assuming you have a MV or HV circuit breaker w/ no "brains", the relay is the brains. So, there will be a slight delay between relay sensing, and the relay issuing a trip command. So it would actually be longer than 2 sec, unless you included the opening time of the breaker.
Mike
There are usually interlocks between a VFD, load side disconnect and the VFD itself (I've never used a starter on the load side of a VFD, but have installed disconnects on the load side of a VFD for local isolation). Drives don't like switching actions on the load side of their terminals while a...
Consider the withstand time of the resistor. A 400A resistor is pretty common, having a 10 second withstand. Extended time ratings means more $$$.
Mike
I use this:
https://www.mitchellinstrument.com/hd-electric-hva-2000-high-voltage-digital-ammeter-up-to-500kv.html?gad_source=1&gclid=EAIaIQobChMI5ZvQ8uesigMVuiytBh3zcxGFEAQYASABEgJz0fD_BwE
Mike
I would just add to dpc's commentary: close-coupled switchgear, i.e. perhaps a power style transformer that is a few feet away from a switchgear lineup, will likely have a SLG fault current (3*Io) greater than the 3PH fault current. As dpc addresses above, this is cause for concern.
Mike
Right or wrong...I used the following:
<5% VTHD
<33% ITHD
Anything above those #'s, I would look into filtering if operational/equipment issues were noticed, etc. I hadn't experienced any operational down-sides to those #'s, but your mileage may vary depending on your installation.
Mike
If I'm not mistaken, if a UPS fails, it will want to transfer from the inverter/rectifier to its static bypass. Maybe this is why the time delay on your UV release didn't work.
Mike
Is the UPS operating in "energy savings" mode rather than double conversion? I wonder if there is some issue w/ syncing as previously mentioned. If it is operating in D-C mode, then maybe an issue with the rectifier/inverter?
Mike