Recent content by mparenteau

  1. mparenteau

    Analysis for determining location of arrestors on overhead distribution lines

    Maybe this will help: IEEE Std C62.22TM-2009 Mike PS Found this paper as well: https://www.sciencedirect.com/science/article/pii/S0378779621005642#:~:text=Line%20surge%20arresters%20are%20installed,to%20a%20poor%20soil%20conductivity.
  2. mparenteau

    Arc Flash in SKM

    Assuming you have a MV or HV circuit breaker w/ no "brains", the relay is the brains. So, there will be a slight delay between relay sensing, and the relay issuing a trip command. So it would actually be longer than 2 sec, unless you included the opening time of the breaker. Mike
  3. mparenteau

    MV Switchgear Fuse

    Who knows? Did you look at how the fuse performs at 12x @ .1 sec and 20x @ .01 sec (I have seen 25x @ .01 sec as well)? Mike
  4. mparenteau

    Single VFD running two motors - One motor temperature much hotter.

    An ID run is a procedure whereby the VFD "learns" the motor(s) characteristics via an algorithm. I'll defer to jraef on the rest... Mike
  5. mparenteau

    Running a DOL starter from a VFD

    There are usually interlocks between a VFD, load side disconnect and the VFD itself (I've never used a starter on the load side of a VFD, but have installed disconnects on the load side of a VFD for local isolation). Drives don't like switching actions on the load side of their terminals while a...
  6. mparenteau

    Eutectic Alloy vs E100 Solid State Overload

    Solid state OLs will give you some flexibility on setting based on FLA. Some have phase loss settings for motor protection as well. Mike
  7. mparenteau

    480V ungrounded Delta

    Thanks to dpc for clarifying. Yes...400A resistor on a 480V system is no bueno. My suggestion is for a MV system.
  8. mparenteau

    480V ungrounded Delta

    Consider the withstand time of the resistor. A 400A resistor is pretty common, having a 10 second withstand. Extended time ratings means more $$$. Mike
  9. mparenteau

    Current clamp meter high voltage

    I use this: https://www.mitchellinstrument.com/hd-electric-hva-2000-high-voltage-digital-ammeter-up-to-500kv.html?gad_source=1&gclid=EAIaIQobChMI5ZvQ8uesigMVuiytBh3zcxGFEAQYASABEgJz0fD_BwE Mike
  10. mparenteau

    3-Phase Faults Vs Line to ground

    I would just add to dpc's commentary: close-coupled switchgear, i.e. perhaps a power style transformer that is a few feet away from a switchgear lineup, will likely have a SLG fault current (3*Io) greater than the 3PH fault current. As dpc addresses above, this is cause for concern. Mike
  11. mparenteau

    Industrial System Harmonics Application

    Right or wrong...I used the following: <5% VTHD <33% ITHD Anything above those #'s, I would look into filtering if operational/equipment issues were noticed, etc. I hadn't experienced any operational down-sides to those #'s, but your mileage may vary depending on your installation. Mike
  12. mparenteau

    ACB trips when the control power transfer from UPS A to UPS B

    If I'm not mistaken, if a UPS fails, it will want to transfer from the inverter/rectifier to its static bypass. Maybe this is why the time delay on your UV release didn't work. Mike
  13. mparenteau

    Low Voltage MCC - Build/Configuration Tool

    You'll most likely have to go through a service sales engineer and they can work it up for you. Mike
  14. mparenteau

    UPS going to Bypass Mode instead of supplying through Batteries.

    Is the UPS operating in "energy savings" mode rather than double conversion? I wonder if there is some issue w/ syncing as previously mentioned. If it is operating in D-C mode, then maybe an issue with the rectifier/inverter? Mike