  1. newelecteng

    In cross bonding, why is there a voltage gradient between grounded and bonded points of sheath

    In a cross-bonded system, the increasing voltage gradient from the earthed point to the bonding point is caused by the induced voltage from the AC current flowing in the cable conductors. While the earthed points hold the sheath at ground potential, the magnetic field induces voltages in the...
  2. newelecteng

    Substation/HV grounding - Please let me know if my understanding is correct

    why current transformers (CTs) shouldn’t be grounded on both sides: 1. Avoiding Ground Loops: What is a ground loop? A ground loop occurs when both ends of the CT secondary circuit (the measuring circuit) are grounded, creating a closed loop through the ground. In such a loop, unwanted currents...
  3. newelecteng

    Substation/HV grounding - Please let me know if my understanding is correct

    1. Grounding Grid Purpose: The primary function of a grounding grid is to protect people and non-current carrying metallic objects, such as poles, towers, equipment enclosures, and switch handles, by keeping the ground potential as close to zero as possible during fault conditions. 2. Fault...
  4. newelecteng

    Overvoltage During Earth Fault

    Stevenal, Do you think we could still experience a neutral shift even with an earthing transformer in place? Beyond8, Do we need to consider changing the earthing transformers?
  5. newelecteng

    Overvoltage During Earth Fault

    plase see attahecd disturbance recoder of the incomer.https://files.engineering.com/getfile.aspx?folder=094eb683-c019-4461-adeb-5613182e251e&file=REF630-AA1MVA01A1_DR111_20240801151724_240922_130224.pdf
  6. newelecteng

    Overvoltage During Earth Fault

    the fault was 10km away plase see attahecd disturbance recoder of the feeder.https://files.engineering.com/getfile.aspx?folder=61cd71a9-8fc9-48d2-a2b7-3f14a07a515e&file=REF630-AA1MVA03A1_DR114_20240801141654_240922_130137.pdf
  7. newelecteng

    Overvoltage During Earth Fault

    The fault happend on outggoing feeder h03 or h04 See the attached sld on my previous reply
  8. newelecteng

    Overvoltage During Earth Fault

    Yup we use our earthing transformer ZNyn1 to feed out 0.4kv system Please see attached SLDhttps://files.engineering.com/getfile.aspx?folder=de666175-3cd2-479b-891e-782a52c1ccdd&file=2GJA321107_RevA_240922_195536.pdf
  9. newelecteng

    Overvoltage During Earth Fault

    Dears We are experiencing an issue where, during an earth fault on our 33 kV outgoing feeder, the voltage measured by the ABB REF relay (Vo) on the incomer spikes to around 14 kV. This overvoltage is affecting our 0.4 kV system, which is fed by our ZNyn1 earthing transformer. Is this behavior...
  10. newelecteng

    YNd11 (earth fault at delta side)

    Thanks all Why we need to ground open delta PT at one corner?
  11. newelecteng

    YNd11 (earth fault at delta side)

    Waaross Is there any chance that charging current will be reflected in the star ground side
  12. newelecteng

    YNd11 (earth fault at delta side)

    Hi all I have YNd11 transformer used as stepdown from 33kv(YN) to 11kv(d) to feed loads in 11 kv side -The question is If we have earth fault in 11kv systems how we can detect it. -is there will be reflection on star side of this earth fault. -Is it possible to have earth fault in this case...
  13. newelecteng

    Parallel transformer synchronization

    So we don't need any synch check in case of identical power transformer closing because there is no phase shift in the secondary
  14. newelecteng

    Parallel transformer synchronization

    So we just close the tie beacker without any synch.