In a cross-bonded system, the increasing voltage gradient from the earthed point to the bonding point is caused by the induced voltage from the AC current flowing in the cable conductors. While the earthed points hold the sheath at ground potential, the magnetic field induces voltages in the...
why current transformers (CTs) shouldn’t be grounded on both sides:
1. Avoiding Ground Loops:
What is a ground loop?
A ground loop occurs when both ends of the CT secondary circuit (the measuring circuit) are grounded, creating a closed loop through the ground. In such a loop, unwanted currents...
1. Grounding Grid Purpose:
The primary function of a grounding grid is to protect people and non-current carrying metallic objects, such as poles, towers, equipment enclosures, and switch handles, by keeping the ground potential as close to zero as possible during fault conditions.
2. Fault...
Stevenal,
Do you think we could still experience a neutral shift even with an earthing transformer in place?
Beyond8,
Do we need to consider changing the earthing transformers?
plase see attahecd disturbance recoder of the incomer.https://files.engineering.com/getfile.aspx?folder=094eb683-c019-4461-adeb-5613182e251e&file=REF630-AA1MVA01A1_DR111_20240801151724_240922_130224.pdf
the fault was 10km away
plase see attahecd disturbance recoder of the feeder.https://files.engineering.com/getfile.aspx?folder=61cd71a9-8fc9-48d2-a2b7-3f14a07a515e&file=REF630-AA1MVA03A1_DR114_20240801141654_240922_130137.pdf
Yup we use our earthing transformer ZNyn1 to feed out 0.4kv system
Please see attached SLDhttps://files.engineering.com/getfile.aspx?folder=de666175-3cd2-479b-891e-782a52c1ccdd&file=2GJA321107_RevA_240922_195536.pdf
Dears
We are experiencing an issue where, during an earth fault on our 33 kV outgoing feeder, the voltage measured by the ABB REF relay (Vo) on the incomer spikes to around 14 kV. This overvoltage is affecting our 0.4 kV system, which is fed by our ZNyn1 earthing transformer. Is this behavior...
Hi all
I have YNd11 transformer used as stepdown from 33kv(YN) to 11kv(d) to feed loads in 11 kv side
-The question is If we have earth fault in 11kv systems how we can detect it.
-is there will be reflection on star side of this earth fault.
-Is it possible to have earth fault in this case...