Hi all friends,
Do you have a circulating fault currents scheme in Star/delta, Delta/star, star/star transformers for differential protection? Circulating directions / current magnitudes...
Also calculations which differential relay calculate.....There s no any details in manuals.
Thanks a lot.
Hi guys,
I was trying to synhronize two lines. Voltage difference-frequency difference and angle difference is almost 0. Values are always within limits. But relay inconsistenly gives Synchron OK.
Sometimes it gives "OK", sometimes NOT. And there s no specific time for giving Synchron OK...
Hi friends,
I would like to ask you a question.
If the residual overvoltage fault occurs on F1 , What will A and B see ? Same residual overvoltage magnitude ? Or Will they see the fault ...
Hi to all,
I would like to ask you a question about routine test of circuit breakers.
I have a Medium Voltage CB to do maintenance. I know how to do contact resistance test, but I checked all standarts and I coulndt find a percentage about approving " Did the test pass or no" .
Do you have...
I was talking about the magnitudes not angles...Because I did not know that is why current occurs on phase C in HV during occuring fault A in LV.
If there is fault on phase A in LV, The fault should flow on phase current A , line current A and line current C. It s what I learned.
Still not...
waross,
Yes I got your point.
By the way,
I find out the problem which I faced.
I just followed the diagrams's explanations in some pics and articles.I saw that they did not point out the Delta connection type.Some of them are DAB, others are DAC connection.
In protection relays I saw the...
veritas , stevenal and waross ;
On first diagram , Current occurs on line A and C ..Yes... But how about phase currents ? If there is a L-E fault on A , Will fault current flow on phase A or phase C? That s the point which I dont understand.
And there is another diagram on attachment. I...
veritas , thank you .
stevenal , I just saw your message.
Can you please check this drawing?
on attachment.https://files.engineering.com/getfile.aspx?folder=c04e8b50-3999-462f-a817-c7768dc16b11&file=111111111111111111.PNG
Hi everyone, sorry for my english..I m not well experienced guy.
I just want to know that is there any much clear document about "current flows and calculations during faults in transformer"
I checked many documents in this forum and in others.But I coulndt find it.
By the way, Can you...