why not use concrete pit walls instead of running cmu all the way down? seems like it might be easier to bring the mason in after pit, pit wall, and sog are poured..
If it makes you feel any better, I can’t figure out why they’re rejecting it (with my limited couple years of design experience). I don’t think the block selection shown would violate any code requirements. Does the block have ASTM certification per the drawings? Block height is typically per...
What I have done before is increase the plan size of the footing by pouring concrete around the footing on 2 or 4 sides, and doweling bottom footing bars into the existing footing that then get 90deg hooked to the rebar in the new portion of the footing.
I often see the Ev added to the dead load, with the factor for the dead load being modified. So if your Ev is .15D, this gets added to the 1.2 to make the dead load factor 1.35D.
If the column is not responsible for resisting any horizontal seismic load (aka not a part of your LFRS), you do not...
My firm uses a bearing plate detail more similar to the one dhengr proposed. We provide nelson studs welded to bottom of the plate, A325 bolts through normal size hole in plate and long slotted holes parallel to beam. These bolts are tack welded to the bottom of the plate for installation...
In 13.2.7.2, it references 7.4.3 which says to take the critical section for shear as "d" away from the critical section for Mu. Wouldn't this be a less Vu than in the Bowles book?
I am in the process of the lateral design of a single story, rectangular, masonry shear wall and wood diaphragm building. The shear load is being transferred to the shear walls from the diaphragm through a continuous wood ledger, and anchors into the face of the masonry wall every so often...