  1. Roukkia

    Below Grade CMU Wall Grouting Requirements

    why not use concrete pit walls instead of running cmu all the way down? seems like it might be easier to bring the mason in after pit, pit wall, and sog are poured..
  2. Roukkia

    16" vs 8" bond beams

    If it makes you feel any better, I can’t figure out why they’re rejecting it (with my limited couple years of design experience). I don’t think the block selection shown would violate any code requirements. Does the block have ASTM certification per the drawings? Block height is typically per...
  3. Roukkia

    Strenghtening Existing Spread Footing

    What I have done before is increase the plan size of the footing by pouring concrete around the footing on 2 or 4 sides, and doweling bottom footing bars into the existing footing that then get 90deg hooked to the rebar in the new portion of the footing.
  4. Roukkia

    Struggling with Basic Masonry Design Problem

    I would compare your calc with the flexure calcs in this textbook https://whymasonry.org/2015dorms/?
  5. Roukkia

    Reinforced CMU Jamb / Column for Lateral and Gravity.

    Are you sure you’re not supposed to be using 32,000psi instead of 60,000psi?
  6. Roukkia

    Seismic Forces and LRFD Load Combinations

    I often see the Ev added to the dead load, with the factor for the dead load being modified. So if your Ev is .15D, this gets added to the 1.2 to make the dead load factor 1.35D. If the column is not responsible for resisting any horizontal seismic load (aka not a part of your LFRS), you do not...
  7. Roukkia

    Steel Beam Bearing Pockets and Thermal Expansion

    My firm uses a bearing plate detail more similar to the one dhengr proposed. We provide nelson studs welded to bottom of the plate, A325 bolts through normal size hole in plate and long slotted holes parallel to beam. These bolts are tack welded to the bottom of the plate for installation...
  8. Roukkia

    critical section for shear (footing with masonry wall)

    In 13.2.7.2, it references 7.4.3 which says to take the critical section for shear as "d" away from the critical section for Mu. Wouldn't this be a less Vu than in the Bowles book?
  9. Roukkia

    critical section for shear (footing with masonry wall)

    hoshang - You would take it at a 45 degree angle from the location indicated in Table 13.2.7.1 of ACI318-14.
  10. Roukkia

    critical section for shear (footing with masonry wall)

    What code are you using? This is directly addressed in ACI
  11. Roukkia

    Long Span Metal Roof Deck (+30'-0" spans)

    dold - they have a diaphragm design manual but you may need to contact them for it, not sure how to post that here either
  12. Roukkia

    Long Span Metal Roof Deck (+30'-0" spans)

    Check out the epic metals catalog, I know this is a thing they have been focusing on in their product line.
  13. Roukkia

    New Opening in Existing CMU Wall - Headers

    drift - why cope the ends of the angles? why not install the angle into the bed joint so then it is a bearing connection to the masonry?
  14. Roukkia

    Masonry shear wall - diaphragm shear calc

    Thanks Dave, that is the answer I was looking for! EZBuilding - yes that is correct. Here is the sketch I promised.
  15. Roukkia

    Masonry shear wall - diaphragm shear calc

    I am in the process of the lateral design of a single story, rectangular, masonry shear wall and wood diaphragm building. The shear load is being transferred to the shear walls from the diaphragm through a continuous wood ledger, and anchors into the face of the masonry wall every so often...