Hi everybody
As you know in a substation automation system we read the metering information via modbus protocol,I would like to know that can we convert modbus to IEC61850 and then transmit the metering information to the system?
Hi everybody
Because of special specification of sealed batteries I have never seen that this type of battery used in power substations.But I want to be sure that can we use this type of battery in power substation or not.Do you have any experiance about this?
Dear scottf
our case is as follow:
400kv substation,400kv/110v CVT,burden of CVT is 10VA,secondary is connected to distance relay(7SA522)& metering equipment,total load is 6VA.lenght of cable is 300meter.We will use cable with 2.5mm^2 cross section.is it correct or not?
Dear scottf
I'm so grateful for your reply.
Do you mean that 1% or o.5% voltage drop is very identical and this can be more?
we define the cross section of the cable as e.g 4mm2 and I didn't undrestand the 10AWG,IF it's posible please explane it more.
thanks a million
Dear 7anoter4
CVT is not used to supply the equipment,motor,...is supplied from the DC supply of the substation or if they need AC supply,this provided from AC auxiliary supply of the substation.As you know CVT is used for protection relays and meters.e.g for input of distance relay,measuring...
hi dear slavag
our lines are parallel,we have coupler.
It's clear that for short circuit lines it's so better to use line differential relay but there is an important parameter that we should consider,"PRICE".if we use line diff. we should use fiber optic cable and this increases the price.so...
Hi everybody
As we know in IEC mentioned that because of keeping the accuracy,load of CVT should be 0.25% to 100% nominal burden of CVT anf If the load is less than 25% nominal burden,accuracy of CVT will reduce.I would like to know that is there any relashin beween load and accuracy,e.g if the...
Hi slavag
Thank you so much for your help.
Our line:cable line,4km,132kv,800A,without autorecloser,there are two line just between two substation,on the other hand this is end substation and is not in a ring of substations.
following to my question,would you tell me less than which distances we should use line differential protection instead of distance relay,e.g less than 10km or 5km or something eles.
Dear scottf,so grateful for your help.I thing we should use TPY class for distance protection in 400kv lines because of DC offset of the current.I don't know that should I do the rule mentioned in IEC 44-6 for Rct or not.I asked CT manufacturer about this but they said that there is no need to...