it will be a solidly grounded system to detect earth faults and the 3.7kA is on the 480V side and not on the 13.2kV side. The 13.2 kV side grid is also built by us and we are the only utility in the rural area.
Thank you for your reply. How is the resistor calculation done and then based on this what will the transformer size if I am to use a zig-Zag transformer. Could you please share a sample calculation if you have it would be really helpful
Hi All, I have a hybrid power plant with PV, Battery and DG connecting to a 13.2 kV grid via a step-up transformer. the 480V side is delta which is ungrounded, how do I size a grounding transformer? the L-G fault is 3.7kA,
Hi All,
We are in the midst of designing a hybrid power plant with solar PV, BESS and DG with a 15kV substation (with step up transformer and MV switchgear). For this to prepare a earthing mesh design as per IEEE 80 could you please let me know if I create an individual mesh for the substation...