Recent content by ShooterBooter

  1. ShooterBooter

    Phase symbols

    You usually want the phases ordered A-B-C from top to bottom or from left to right. The "symbol" is not an actual symbol, it's just three lines crossing each other. I attached an alternative to how to draw the circuit...
  2. ShooterBooter

    Time interval for measuring transients in SCADA

    No SCADA system is designed for transient fault measurement. Either you adapt the solution proposed by ZapSib or you need to find an external TFR. Here's a couple readily on the market: siemens abb -SB
  3. ShooterBooter

    PT Secondary Fuse

    1. You need to ground the neutral on the PT primary side. Without a grounded neutral you will not get a earth fault relay to work trough the PT. I assume the network is isolated or hiZ earthed. -SB
  4. ShooterBooter

    ABB REF542Plus

    Can't you use PCM600? -SB
  5. ShooterBooter

    Ground Fault Detection on secondary of wye-wye transformer

    The standard zero sequence impedance measurment/test won't detect this since the primary neutral is used as return path. The only way to test this should be by applying 3-phase voltage on the primary terminals with the primary neutral unconnected and one secondary phase shorted to neutral, the...
  6. ShooterBooter

    Ground Fault Detection on secondary of wye-wye transformer

    I can't really recall seeing any test records mentioning any tests done to verify this "feature". Anybody else seen this? -SB
  7. ShooterBooter

    Ground Fault Detection on secondary of wye-wye transformer

    Ungrounded wye/grounded wye transformer will definitely provide path for zero sequence flux to flow for line to ground fault on secondary side.The flux path is via the tank of the transformet for core type transformets.Zero seq impedance is typically in the range of 50% to 100%. No,you don't...
  8. ShooterBooter

    Cable sizing

    bee79; I think both 10kA and 20kA are a bit too even and round to be the actual short circuit current. I suppose that these are each panels rated s.c.c.? You really need to calculate the actual s.c.c. in the lighting panel. Alajji; To ensure discrimination of CB on individual circuit , the...
  9. ShooterBooter

    Cable sizing

    As Bill wrote; It depends. Total discrimination means that no matter how high short circuit current you have (up to max rated s.c. current of the MCCB/MCB) the downstream device will always trip before the upstream. There is seldom need for total discrimination; if you know the value of the...
  10. ShooterBooter

    Understanding delta VT ratios

    Veritas, The phasor diagram(s) can be thougth of as a representation of the VT windngs, nothing virtual about that. Regarding the other issue of phasor voltage being negative; I would say no, it's not negative. IF it were negative the phasor arrow of phase "a" would point towards the neutral...
  11. ShooterBooter

    How to lock out remotely controlled circuit breaker in OFF position?

    Sorry, missed that (on My Iphone, small screen...) You can't disconnect aux power to the CB and thus making it inpossible to operate? -SB
  12. ShooterBooter

    Understanding delta VT ratios

    There, I "cleaned" up my scribbles. Enjoy. -SBhttp://files.engineering.com/getfile.aspx?folder=a4653fb3-ee7e-40d5-9174-5dbd240146af&file=thread238-405639_r1.pdf
  13. ShooterBooter

    Understanding delta VT ratios

    Veritas, Yes, you're right. Actually that part should indicate the pre-fault conditions. I'll correct that and post a new verion later today. I also need to correct the calculations on page two; I'm missing a "3" in the middle part. It doesn't affect the outcome though. -SB
  14. ShooterBooter

    Understanding delta VT ratios

    Veritas, Glad to help. -BAK