  1. wcaseyharman

    Generator Protection - Selection of Fuse based on Sustained Current

    Yes, the current away from the generator will be lower. The curve referenced earlier is a bit tricky because it appears to include the dynamic response of the exciter. What this means is the fault voltage driving the fault current is varying. Depending on what you trying to do this may or may...
  2. wcaseyharman

    Generator Protection - Selection of Fuse based on Sustained Current

    It depends. On a close in bolted 3PH fault an instantaneous breaker would likely trip. A single phase fault away from the generator might not generate enough current to trip the instantaneous element, and if it’s tripping on the breaker thermal curve then I would expect it to be in the sustained...
  3. wcaseyharman

    To replace faulty power alternator with a smaller unit

    Depending on interconnection requirements you may need to keep in mind VAR capability and may need to run the turbine at an even lower load to provide VAR headroom - our transmission providers require 33% VAR capability at full load. Some generators have curves available to increase output on...
  4. wcaseyharman

    2MVA generator

    A couple of thoughts: 1. Since V = d_phi/dt, voltage should be linear with speed with a fixed magnetic field. What voltage do you need? 2. That sounds complicated since you’d generally need to rotate the machine - shiv and belt drive with a pony motor? Is this a bust fed excitation system...
  5. wcaseyharman

    Generator with low IR

    Neta MTS-2011, page 135, section 7.15.1 has the following guidance: - 1megohm per kV on armature windings made before 1970 and field windings -100 megohms for ac and dc armature windings made past 1970 (form wound) -5 megohms for random wound coils and form wound coils below 1000V. This...
  6. wcaseyharman

    Generator with low IR

    For low voltage equipment I generally see the pass/fail at 1 megohm, with I think comes from a NETA (inter-National electrical testing association) testing guideline. I don’t remember the section, if you’re interested I can go back and find it and get you the reference. Casey
  7. wcaseyharman

    Reactance and Time constant tests for a generator

    In larger machines originally WECC, and now NERC, require validation of those generator parameters to ensure accurate grid stability models. System protection also uses them to provide accurate fault currents in system fault programs such as ASPEN Oneliner. However, NERC registration starts at...
  8. wcaseyharman

    Query on grounding of VT primary side

    There are various reasons why a designer chooses different VT grounding methods: - the grounding of the power system neutrals can be different. - the protection methods are different - different sets of VTs are used for different things. - design standards from different engineering groups favor...
  9. wcaseyharman

    Question about LTC Transformers

    Biggest impact of LTCs I think of on IBRs is the loss of VAR capability at high voltage. If the taps aren’t set right the VAR capability can be severely limited. Right now for that reason I plan to set the LTC in our new wind farm to manual - I just don’t see much value in the LTC anymore with...
  10. wcaseyharman

    Doble Tests of Power Transformer

    We use power factor testing as part of a GSU testing plan, along with turns ratio tests and dissolved gas analysis.
  11. wcaseyharman

    Fault current capability of DFIG generators

    I’m working on relay settings for a type 3 wind farm. According to the manufacturers literature, the rotor inverter controls the fault current of the generator unless the voltage across the electronics get too high, then a crowbar operates to short the rotor circuit and protect the rotor...
  12. wcaseyharman

    KW, KVA, KVAR relationship

    Here’s how I think I would go about calculating losses and seeing if I could get some savings in energy: Let’s think about the generator only (put a reactor off your switchgear) for simplicity. This is how I would go about it: Losses are I^R. If you get the R off the generator datasheet...
  13. wcaseyharman

    Paralleling dissimilar Generators

    I defer to your experience, I’ve done a few islands/Microgrids but most of my experience is with larger grid tied units.
  14. wcaseyharman

    Paralleling dissimilar Generators

    Generally you want fast acting governors and AVRs to maintain consistent voltage and frequency to the load. I wouldn’t advise block loading or PF mode. (The US western grid tried something similar in the 1990s and dumped California in the dark. It was shortly after that PF and VAR modes were...
  15. wcaseyharman

    Optimal value of Sub transient reactance - Generator

    that is a very interesting question - from the power grid perspective subtransient reactance and resistance provide damping to power system oscillations. I’ve only known that you have to watch out for it being too small and overdutying the connected interrupting device, but very curious how...