  1. wcaseyharman

    Optimal value of Sub transient reactance - Generator

    that is a very interesting question - from the power grid perspective subtransient reactance and resistance provide damping to power system oscillations. I’ve only known that you have to watch out for it being too small and overdutying the connected interrupting device, but very curious how...
  2. wcaseyharman

    Neutral Grounding Practice for Utility Pad Mount Transformers

    I understand my utility does exactly as you describe - neutral is tied to the transformer tank and to the vault ground, as well as the customer neutral (and by extension the customer’s ground)
  3. wcaseyharman

    Analysis for determining location of arrestors on overhead distribution lines

    My utility locates arrestors on substation equipment (transformers) and on underground terminations. I don’t believe we use them anywhere else - granted, we get very little lightning.
  4. wcaseyharman

    Paralleling dissimilar Generators

    In my region, the western us, the regional planning entity (Western Electric Coordinating Council) has a guideline for frequency droop from 3-5%. We’ve set our larger hydros at 3% to improve the frequency response in our balancing area. Gas turbine droop typically is 4% and it’s trickier to...
  5. wcaseyharman

    Paralleling dissimilar Generators

    Droop is your friend. Use frequency droop. 3-5% is typical. If the units connect to the same bus without transformers, assuming the units are in voltage control, use voltage droop to prevent the AVRs from fighting each other. You might use an external voltage setpoint once the units are online...
  6. wcaseyharman

    Auxiliary Motor Speed Impact on Transient Undervoltage?

    Good point, that would provide much better response for longer duration sags. The high level study I mentioned earlier was using modeling tools (Aspen Oneliner). We have not done it in my company, largely because I work in the generation side of a utility where we have 30MW to 200MW generators...
  7. wcaseyharman

    What is positive to negative sequence coupling and negative to positive sequence coupling ?

    Well, I stand corrected - I should more accurately have stated it’s never come up in my utility that I know of. Load imbalance, now that comes up all the time.
  8. wcaseyharman

    Auxiliary Motor Speed Impact on Transient Undervoltage?

    I wonder if it might be economical to increase the bus voltage during voltage sags rather than modify motor starters and risk stalling (I’m not sure how many motors you are talking about). Synchronous motors/generators, synchronous condensers and STATCOMs can inject reactive power during low...
  9. wcaseyharman

    Switchgear busbars sizing

    I would assume manufacturers would consider the worst case or most conservative case when designing switchgear - that the main bus can handle all the attached load. This would be common on a main tie main system - two 1200A mains with a 1200A tie supplying <1200A of load. Your situation is a bit...
  10. wcaseyharman

    What is positive to negative sequence coupling and negative to positive sequence coupling ?

    I’m not clear what you are trying to do, but by your terms I am assuming you’re connecting to a distribution circuit. The utility assumes their lines are perfectly transposed, which they are not, but the voltage imbalanced caused by balanced load on a poorly transposed distribution circuit is...
  11. wcaseyharman

    Arc detection relay Vs UFES (Ultra fast earthing switch)

    Tripping an upstream breaker faster will reduce the process impact on the rest of the plant and reduce potential equipment damage by removing the fault quicker. I would tend toward fast arc detection relays unless I don’t have access to the upstream device or it’s a fuse.
  12. wcaseyharman

    Types of battery used in UPS and Electrical Substations

    100% flooded lead acid at my utility (medium sized US utility, about 1.2 million customers) for substation and generation control and relay systems. Require maintenance, but highly reliable, we had bad experiences with VRLA in the past (battery failure caused a coastdown without lube oil on a...
  13. wcaseyharman

    On ferroresonance damping resistor

    Parallel. The relay is measuring the voltage drop across the resistor to detect 3Vo to determine a ground fault or to polarize directional elements. This set up with the resistor in the delta (in USA called a Broken Delta) of a PT secondary is ubiquitous on utility sized generating stations.
  14. wcaseyharman

    AVR VT Location

    For utility scale generators we have examples of both at the company I work at, and operationally I don’t notice a difference. It seems more common to put the PTs in the switchgear with the breaker - often the gen and line PTs used for synchronizing are in the same cabinet.
  15. wcaseyharman

    GCB in the 15,000 Amp range

    In the generators I work at, which are mostly gas and smaller steam turbines, plus some medium sized hydro, vacuum dominates up to a 5000A ampacity, above that it goes to SF6. We had some magnablast air breakers, and some of the older hydros had air breakers, and even a couple of oil breakers...