  1. wfeldmann

    pitot tube flow measurement

    We did find the problem and it was in the parameters of the DP transmitter. It had to deal with the square root and linear settings and values assigned to these parameters. By the way it was a prandtl tube I was using and I had it hooked to a yokogawa pressure calibrator, so I could get static...
  2. wfeldmann

    pitot tube flow measurement

    I am using a pitot tube connected to a differential pressure gauge and I get the following readings. The static pressure (perpendicular) was connected to the low side and the total pressure (parallel) was connected to the high side of the gague. Dp static Total 30Hz -...
  3. wfeldmann

    Orifice sizing

    Yes and thank you for finding that mistake with the ID for the tubing it caused us to re-evaluate what we can use. We are thinking of taking the restriction orifices out and replacing them with needle valves, because we have so many unknowns and some of the process values we got I don't trust...
  4. wfeldmann

    Orifice sizing

    I am in all three phase of the project. We have just finished design and we are currently in fabrication and in 3 months will be testing. Each 3/8" run is 25 feet in length and the 3/4" run is about 15 feet.
  5. wfeldmann

    Orifice sizing

    What is a slinted bronze filter? How exactly would this work and would you have to worry about contaminants over the long run? I will look it up and thanks for the option.
  6. wfeldmann

    Orifice sizing

    All runs are new and there are a total of 8 - 3/8" tubing runs that cool the bus bar. There are two zones per chamber and each zone has a positive and negative bus bar and the tubing is run on boths sides of the bus bar for a total of 8. From our bus bar heat calculation that mechanical...
  7. wfeldmann

    Orifice sizing

    Latexman, You have been very helpful and I appreciate it.
  8. wfeldmann

    Orifice sizing

    Pertaining to katmar's question. Is the 0.5 psi pressure drop the permanent pressure drop (i.e. are you designing a restriction orifice) or is this a flow measuring orifice with close tapping points? Yes, it will be a permanent pressure drop with a constant pressure supplied from a header that...
  9. wfeldmann

    Orifice sizing

    You were correct I forgot to take the square root of the entire equation. Basically if I increased the pressure drop across the orifice I will lower my diameter. If I increased my pressure drop from 0.5 psig to 3 psig I would get a diameter of approx. 0.25". Pressure (psi) = (Head * Specific...
  10. wfeldmann

    Orifice sizing

    Thank you for your response and clarification. What I am trying to maintain is a 2 gpm flow rate, but it does not have taps. This flow is through a 3/8" SS .065" wall thickness tubing and I was going to use a swagelok union with orifice inside the union to control the flow. That is why I am...
  11. wfeldmann

    Orifice sizing

    Does anyone know who to size an orifice with the following parameters. What I am trying to find is the diameter of the orifice I need to have to drilled in a orifice plate in a swagelok fitting to allow 2 gpm flow with a .5 psig drop and the fluid is DI water. The value I came up with was 0.153...