Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by wpuryear

  1. wpuryear

    100kw asynchronous generator power factor

    So what would be possible causes of the doubled reactive load? Walt
  2. wpuryear

    100kw asynchronous generator power factor

    The 480 measurement is before we go through two transformers - 480 to 4200 and then 4200 to 42k. Our synchronous 2mw generators runs at 4200 but is currently off line for lack of water. I might add that field coil temperatures are in the 165 to 170 F. range. So, is the low power factor simply...
  3. wpuryear

    100kw asynchronous generator power factor

    I thought generator terminal voltage was determined by the grid voltage. At any rate, I'll read the values in the A.M. Walt
  4. wpuryear

    100kw asynchronous generator power factor

    Nameplate voltage is 480 Operating voltage is 480 +/- and is determined by grid voltage Current on generator leads are 225 amps Current on grid leads are 128 amps Current on capacitor leads are 167 amps Power factor on generator leaks is .57 Power factor on grid leads is .98 Rated output is...
  5. wpuryear

    100kw asynchronous generator power factor

    It's not a wound but a squirrel cage rotor. It just seems to me that .57 is an awfully low power factor (name plate is .80) and I'm trying to learn why. The unit was not operational when we purchased the plant due to a short caused by water infiltration, but as I recall, there were...
  6. wpuryear

    100kw asynchronous generator power factor

    The turbine and asychronous generator are totaly submerged and the capacitor bank is not. Current between generator and capacitors is 225 amps, however power factor correction with capacitors reduces this to 128 amps going to the grid. A better generator power factor would reduce the reactive...
  7. wpuryear

    100kw asynchronous generator power factor

    I have a water turbine driven submerged 100kw induction generator that was rewound a couple of years ago. Power factor is running at .57 which we are correcting with capacitors, however the high current between generator and capacitors is causing heat problems. The field connections are 12...