fire water demand
Cris-w
Industrial
Nov 7, 2024
14
hi everyone
I have a newly built steel plant building equipped with standpipe system、automatic sprinkler system, and outdoor fire hydrant system. How should I determine the maximum water demand of this building? Should I add up the water demand of each system? Especially, how to determine the water demand of the outdoor fire hydrant system?
Advance thanks!
It should be in your fire code. See for example NFPA 1, chapter 18.
I'm very sorry. After reading NFPA 1, I feel that it doesn't clearly specify this. Maybe I just didn't notice it. Could you give me some more hints? Thank you.
So the building is already built and in operation???!
If so why the question
No, it's just that the construction has just started, but now we need to select the specifications of the fire pump. I haven't found any instructions on how to calculate the flow rate of the fire pump in NFPA. I'm very anxious and hope to get some help.Thanks a lot.
I hold a NICET IV in fire sprinkler layout with 50 years experience.
While I know what fire flow is and means I would NEVER do the calculations because it isn't my job.
The responsibility of calculating fire flows is the job of the registered architect, licensed civil engineer or professional engineer on the facility and not the fire sprinkler designer for the project.
I have seen different states do it differently and I just don't want to go there.
From NFPA https://www.nfpa.org/news-blogs-and-articles/blogs/2022/03/22/calculating-the-required-fire-flow
soory,you mean to determine the flow rate of the fire pump based on this?
What is your occupation?
There are to many variables to get an answer here.
You have to figure fire flow for the building, water supply either public or tank or other, fire sprinkler system demand. Not sure why a standpipe is involved.
I am mainly engaged in the fire protection design of power plants. According to NFPA 850, the water supply demand is calculated by adding 500 gpm to the flow rate of the largest system. However, this is a steel mill, and I haven't found the specific requirements of NFPA for it.
I am not qualified to answer this question but here goes anyway from the way I understand it to be.
What matters the size of the building and if the building/property has sprinklers. If the building has sprinklers the fire flow might be 1,000 gpm if if the building is not sprinkled the fire flow might be double to 2,000 gpm. The way I understand it is it has nothing to do with the sprinkler design, the number of systems or if it has a standpipe or not.
Maybe try this https://www.omnicalculator.com/construction/fire-flow
Key Considerations
Simultaneous Use: NFPA 1 requires the water supply to meet the maximum combined demand of all systems operating together.
Hydrant Fire Flow: Represents manual firefighting efforts and is calculated separately but often reduced for sprinklered buildings.
Standpipe vs. Hydrants: Standpipes (internal) and hydrants (external) are distinct; their demands are typically additive.
For precise compliance, consult NFPA standards and local fire codes.
Is this in the U.S.?
Do you know a fire protection engineer, that knows hydraulics, that can help you
I highly suggest you contact a competent fire sprinkler contractor or a competent fire protection engineer. Site fire flow, standpipes and sprinklers are individual demands. They are not required to be compounded, unless you have an authority (local code enforcement, insurance, etc) that requires it. Typically, fire pump capacity is going to be driven by the site fire flow demands. Pump rating will be typically driven by the standpipe pressures or sprinkler system pressures, whichever is greater.
However, you really need to engage the help of a licensed professional that you are paying for their advice. If you are tasked with doing this work, it would not be my recommendation to take it from some forum online.
In my opinion a fire sprinkler contractor, or designer regardless of his experience, has no business attempting to calculate "fire flows".
How do you work this one?
Its a series of condo's where the design is NFPA #13R in the units and NFPA #13 in the parking garage designed to a OH1. Design in the parking garage is .15/900 as the ceiling height does not exceed 10'-0".
The public water supply is 63 static, 35 residual flowing 700 gpm. We have al seen better. Oh, and I didn't have to add domestic water to my calculations as the 4" watermain you see is solely dedicated to fire water.... domestic water is on another line.
Barely enough for sprinklers, I made it work, but what about the "fire flows"?
The professional engineer used a "private fire well" for his calculations on the required fire flow.
Oh and as you can see sprinklers are really helped because the AHJ requires all systems to have RPZ backflow assemblies so there goes 8 psi off your calculations.
These drawings are sealed and signed so it is non of my business for as far as sprinklers are concerned I am good to go with the fire sprinkler.
So, what is the deal on a "fire well"?
Is this a rural project? You can get some pretty low fire flow requirements on rural projects. Parking garages have been upgraded to OH2 in NFPA 13, 2022 and newer.
If this is a multi-building complex and you have a flow test at the street as it comes to the property, my opinion is that you must include the domestic allowance where the lines meet. If you have a dedicated fire line, they will meet at the city main. But, let's say you are putting 20 buildings on this site. A fire in bldg #1 is going to have no impact on the residents of most other buildings using water and depleting the available water supply. Assuming a small demand of 50gpm per building, that would be 950 gpm demand as a "domestic allowance" at your POC to the city main.
If this were an existing complex, you would get your flow test at a time that would account for all of these buildings in use and consuming water. But since it is just in plan stage, you need to model that domestic use. At least, that is my conservative opinion.
Travis,
This is sort of a rural project where we have a 6" city water main where a dedicated 6" line.
The local fire official has approved the fire flow submitted by a licensed professional engineer so I am good to go.
Usually the word fire flow is the required flow from fire hydrants outside a facility for manual firefighting. This is based on building area and construction type using NFPA 1 or the IFC Appendix B.
When I hear the word fire water demand that normally means interior water demands for active fire protection systems like automatic fire sprinkler systems and standpipes. This is the sprinkler demand plus hose stream or standpipe demand.
The two don't need to be added together, but are considered separately.
In my opinion, and just my opinion, a fire sprinkler designer should have nothing to do with calculating fire flows because they are not related EXCEPT if a building has sprinklers there is a percentage reduction allowed.
It is also my understanding that the method to calculate fire flows can vary between jurisdictions.
What might be required in California might not match what is required in Nebraska?
You are correct. NFPA 1 and the IFC give a fire flow decrease if the building is sprinklered. Typically a civil or fire protection engineer calculates the required fire flow for a building.
And yes, the required fire flow can vary quite a bit depending on the jurisdiction, adopted codes, and other factors.
