    Two-wire 4-20mA specs / expectations below 4 mA

    I believe schlebda's question actually raised 2 points 1st, "Is there an industry standard or performance expectation for 2 wire 4-20mA output devices (actuators, positioners) for signal levels below 4mA?" This answered by Postdanw2, Yes, there is a Standard laid down by NAMUR and Nearly all...
  2. Standingback

    electromagnetic flowmeter for partially full pipe

    The ability of a magflo meter to measure flows in partially filled pipes is heavily dependent on the design of the coils in relationship to the pickup electrodes. I only have limited experience on actual applications, but believe that the Toshiba make a specific meter for this application that...
  3. Standingback

    Level measurement using dP cell transmitter

    I agree with Roydm/LJseagull, but remember that if you use a wet leg reference (figure A3)on the HP and connect the LP to the stack, the output of the transmitter will be inverse to the level. I trust this helps, Mlv http://www.coulton.com
  4. Standingback

    HP Drum level measurement

    Jim, I am unsure how you come to a SG of 0.667 At 115 Barg in the drum. The "water" in a steam drum is actually a bubbling mix of water and steam. The density of which is totally unpredictable and changing as steam bubles are released off the tubes in an uncontrolled manner. To add to the...
  5. Standingback

    Can i get two 4-20ma output signals from one PTx

    Sorry, I had assumed that we we talking in general terms about splitting a 4-20mA loop. To implement this technique within a control loop the diagram would be modified as per the attached. Thanks Roy for preventing further confusion. I trust this helps, Mlv...
  6. Standingback

    Pls address

    I completely agree with JLSeagull. Change to electronic tranmsiiters and valve positioner. I trust this helps, Mlv http://www.coulton.com
  7. Standingback

    Can i get two 4-20ma output signals from one PTx

    The lowest cost option is to wire the control valve and the PLC in series with the transmitter 4-20mA loop There are two issues to watch out for:- 1. That the total loop resistance remains less than 600 Ohms.(which shouldn't be difficult) 2. Wire the PLC in the loop after the valve positioner...
  8. Standingback

    Flow of steam service

    If there is a 3 valve manifold fitted to the transmitter then the increase in temperature could be due to the equaliser valve not seating correctly. I suggest that you isolate the transmitter at the 3 valve manifold and attempt to ensure there is no flow through the impulse lines. Roy may be...
  9. Standingback

    HP Drum level measurement

    I agree with Roy that the issue is the the density of the water in the drum. The article that Roy refers to is very useful and confirms my suggestion that balancing the steam flow against the water flow should be used as the primary measure for level control (see figure 2 in the Tyco article. In...
  10. Standingback

    Contorl Valve Help

    A simple transfer block with a digital flag from a Bialey DCS, will not normally product a mA output . So if your "elctro pneumatic acutator" is actually an electro pneumatic valve positioner. Then you will not have achieved anything. I accept that if your "elctro pneumatic acutator" has a...
  11. Standingback

    Brine flow measurement, non-contact

    I apreciate that experience often leads us to make rational decisions, but my experience of current time of flight and even dopplar devices is that modern devices are head and shoulders above similar technology of 5 yrs ago. so my opinion has changed with time. I would suggest hiring a trial...
  12. Standingback

    Contorl Valve Help

    The answer is, .... two wires. However it would be good to know what you meant by "elctro pneumatic acutator" as this could be loosely interpreted as a solenoid (on off in nature), or e/p positioner (modulating in nature) If it is the former, then you will need a relay output from the DCS...
  13. Standingback

    Intrinsic Safe Wiring to Instrument

    IS by definition stated that the components within the enclosure do not store enough energy to cause ignition. Adding extra cable entries does not effect the IS rating. I trust this helps, Mlv http://www.coulton.com
  14. Standingback

    HP Drum level measurement

    I do not accept the argument that DP transmitters have a problem with pressure. For example the Fuji Electric FCX series transmitter is now capable to operate with a static pressure of 1035 Barg without adverse effects on the accuracy. I believe that the issue is a function of definition. The...
  15. Standingback

    4-20mA Loop Powered Sensor/Transmitter Calibration

    I guess that what we are all trying to achieve is getting a true measurement from the transmitter? I agree that manufacturer calibration equipment is at least one order of magnitude more accurate than any local site standard. But the manufacturer is unable to predict installation effects. These...
  16. Standingback

    One thermocouple feeding two devices

    Dear All, Just to add to Keith's view and perhaps to put some figures on "itty bitty", A "type K" T/C operating at 360 Deg F would produce 6.094 mV. A 4 degree change in temperature (just over 1% increase in temp) produces 6.183mV. So 0.089mV (1.46% change in mV). So even if the imput...
  17. Standingback

    DP transmitter impulse line purging

    Following on from Jims comment, purges lines have been used for a long time. But I note that only continious purge and capilary systems have been mentioned. Continiously purged impulse lines are useful especially in gas measuring, or liquid level allplications(bubbler). Remote seals on dp...
  18. Standingback

    Dual (stacked) DP Flow Transmitters

    Kevin, I guess you already have the flow element, and you are just trying to get the best rangeability from it? So replacing it with another type of flowmeter may not be practical if you cans shut down the line. You have not given us any flow rates, pipe sizes, pressures or temperatures, so it...
  19. Standingback

    Converter RS232 to analogue 4-20mA

    Max, All of these guys have valid points, but it won't matter which way you decide to go, ie RS232 to 4-20mA, RS232 to Ethernet, RS232 to RS232 PLC input even RS232 to Or anything else. There are manufactures that will come up with some black box to convert from one to the other. But they...