Does someone know reference to an international standard like IEEE or IEC that could help in determining the time period that should be used for calculating the demand factor of a motor? Also, does any standard allow applying demand factor to motor FLA's for voltage drop calculations? I am in...
Does anyone know if any institute provides training in API RP505 standard - American Petroleum Institute's recommended practice for classification of locations for Electrical Installations at Petroleum Facilities Classified as Class I, Zone 0, Zone 1, and Zone 2?
Hello,
I am trying to add an additional load to a MCC switchboard that has a bus bar rating of 800A. I want to verify if adding the load will lead to exceeding the capacity of the bus bar rating or not. I am in Canada and the code that I follow is Canadian Electrical Code part 1.
Sum of the...
Hi
Does anyone know if there are any specific IEC standards which has guidelines for assigning tags/names to electrical symbols?
For example, CB for circuit breaker, CR for relay contact, XF for transformer etc.?
I referred IEC 61082 & IEC 60617 and couldn't find any specific information...
Hello
I am conducting an arc flash study of a power distribution system using IEEE 1584. For calculating the arcing current, I need to determine what's the available bolted three phase short circuit current. How is this determined? Is it the utility that provides this parameter? Does this value...