How do you calculate the current on each line conductor for a resistive load?

The load is single phase, 575V Line-Line, 1000W Resistive

I = 1000W / 575V / 1.73 = 1.005A

or is it

I = 1000W / 575V = 1.739A because it's single phase?


Is it correct to call it a single phase load because it's only connected to 2 out of 3 phases at the supply?

 
Replies continue below

Recommended for you

Yes, it's called a single phase load as well. As Lionel implied, your second answer is correct.

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
If there are two 1000W 1-phase resistive loads, across phase A & B and phase A & C.

Does it mean phase A will carry a load of I = 1000W / 575V = 1.739A * 2 = 3.478 amps

phase B & C will carry a load of I = 1000W / 575V = 1.739A = 1.739 amps

Thanks guys
 
Not quite. Phase A will carry 1.739 * sqrt(3) = 3.012 amps
IA = IBA - IAC vectorially
 
jghrist is correct in that the two load currents are 60° apart (from the point of view of phase A), so instead of 2*1.739 it's sqrt(3)*1.739 for phase A current.

All phase currents have to sum to zero as usual, so IA = -IB - IC. But magnitude of phase B and C currents is as you describe - the load current of 1.739A.
 