I have been tasked with role of quality manager for repaving of aircraft taxiway. My company is the GC.
My background: CSM Degree OSU 2012, 5 years ACI field geotech, lab rat.
Spec book indicates the following:
3.14.3.3 Subgrade for Airfield Pavements
Compact top 24 inches below finished pavement or top 12 inches of subgrades, whichever is greater, to 100 percent of ASTM D1557; compact fill and backfill material to 100 percent of ASTM D1557. Core of Engineers spec is actually 95-100%.
Plan book calls for 95% on foundations however road base is usually not considered foundations but rather a portion of the roadway.
Material is State Spec Road Base. T-180: 139.0@6.3, ASTM D1557C Modified 138.2@6.9 and rock corrected 142.9@5.7%.
Subgrade is a poorly graded sand. Very little to no clay. I estimate around 125lbs at 10% or greater optimum moisture. Good stuff as long as it has moisture in it. Holds up fully loaded dump truck with marginal rutting.
I have another 1557 proctor in process with another lab.
We are getting 96-98% and within 1-2% moisture using nuclear density tesing in the field on a 12" layer of road base using 142.9. I have always operated under the notion anything at 100% or greater is usually due to a change in material density beyond what was ran for the proctor, an error in the gauge, or a combination of both. Proof roll gives virtually no rutting or pumping.
I do not want to present "failing" density tests (<100%) to the design engineer however I believe getting EVERY density test to read 100% is not only un-obtainable, but also hard to believe even if we do achieve it. You can turn a density gauge 90* and get different readings...
So which is right? My spec book, the plan design criteria? Is the excerpt in the spec book out of context? DO i have a case to argue or at least get a more clear requirement for compaction?
Thanks!
My background: CSM Degree OSU 2012, 5 years ACI field geotech, lab rat.
Spec book indicates the following:
3.14.3.3 Subgrade for Airfield Pavements
Compact top 24 inches below finished pavement or top 12 inches of subgrades, whichever is greater, to 100 percent of ASTM D1557; compact fill and backfill material to 100 percent of ASTM D1557. Core of Engineers spec is actually 95-100%.
Plan book calls for 95% on foundations however road base is usually not considered foundations but rather a portion of the roadway.
Material is State Spec Road Base. T-180: 139.0@6.3, ASTM D1557C Modified 138.2@6.9 and rock corrected 142.9@5.7%.
Subgrade is a poorly graded sand. Very little to no clay. I estimate around 125lbs at 10% or greater optimum moisture. Good stuff as long as it has moisture in it. Holds up fully loaded dump truck with marginal rutting.
I have another 1557 proctor in process with another lab.
We are getting 96-98% and within 1-2% moisture using nuclear density tesing in the field on a 12" layer of road base using 142.9. I have always operated under the notion anything at 100% or greater is usually due to a change in material density beyond what was ran for the proctor, an error in the gauge, or a combination of both. Proof roll gives virtually no rutting or pumping.
I do not want to present "failing" density tests (<100%) to the design engineer however I believe getting EVERY density test to read 100% is not only un-obtainable, but also hard to believe even if we do achieve it. You can turn a density gauge 90* and get different readings...
So which is right? My spec book, the plan design criteria? Is the excerpt in the spec book out of context? DO i have a case to argue or at least get a more clear requirement for compaction?
Thanks!