Is there a fuse not normally seen in North America that would be used on 1000VAC motors? The only options I'm finding are 1000VAC rated semiconductor fuses or the 3" diameter x 10" long, 2400VAC, R-rated motor fuses.
 
Replies continue below

Recommended for you

Damn, ScottyUK beat me to it.

Older Joy mining machines (and a lot of similar ilk) are 1000V. An ex-employer of mine used to make soft starter controllers for Joy, we used the Siba fuses because there was no room for R type 2400V fuses.