ashtree
Bioengineer
- Nov 28, 2015
- 702
We are working through the issues on installing 1000 volt motors on well pumps at about 350 metres (1100 feet ) below ground. We have to go to 1000v because of the cable size required to limit the voltage drop at 400volts is so large that we cant fit the pump and the cable down the well. These are motors in the 110kw range.
These motors would likely be on VFDs which open up some real challenges but there does not seem to be consensus around which is the best spot to mount the step up transformer:
1) Use a standard voltage VFD and boost after the VFD fitted with some serious sine wave filters, or
2) Step up to 1000volts pre VFD and obtain or specially engineer a 1000 volt VFD.
It seems that both options are possible.
There are limited options for the 1000 volt VFDs off the shelf and at least one standard voltage VFD manufacturer modifies a seemingly standard drive to take 1000 volts. From a spares and redundancy viewpoint this would seem to be the worst option.
The step up transformer after the VFD will possibly have some similar issues and there are obviously efficiency and harmonics etc issues with the arrangement.
I would be interested in hearing anyone's experience or opinion on either of these or other options that i might not know about.
These motors would likely be on VFDs which open up some real challenges but there does not seem to be consensus around which is the best spot to mount the step up transformer:
1) Use a standard voltage VFD and boost after the VFD fitted with some serious sine wave filters, or
2) Step up to 1000volts pre VFD and obtain or specially engineer a 1000 volt VFD.
It seems that both options are possible.
There are limited options for the 1000 volt VFDs off the shelf and at least one standard voltage VFD manufacturer modifies a seemingly standard drive to take 1000 volts. From a spares and redundancy viewpoint this would seem to be the worst option.
The step up transformer after the VFD will possibly have some similar issues and there are obviously efficiency and harmonics etc issues with the arrangement.
I would be interested in hearing anyone's experience or opinion on either of these or other options that i might not know about.