Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

10kv ductor testing 1

Status
Not open for further replies.

DaCaone

Electrical
Jan 21, 2016
1
I know there is no minimum value for contact resistance measurement but with 10kv bus bars are there any guidelines or rule of thumb values as I have no manufacturers information or just go by 10 micro ohms
 
Replies continue below

Recommended for you

Depends on what size bar you're looking at. A 400A distribution switchgear busbar will measure differently to a 20,000A generator main output bus: on the latter I'd be concerned about anything in the 10u[Ω] range, but on the former I'd be quite happy.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor