I have had 2 11 kw 2 pole pumps burn out at the same time.
Both had a converter starters and were found to be connected in star.I have wired the replacements in delta and run no problem.
The motors were 400 v delta 660-690 star.
The manufacturer is insisting that the connection in star would not cause them to burn out but as I understand running at 400 v in star is running undervoltage and not only would the the torque be reduced but this would cause increased temperatures in the windings.
Any technical info to give to the manufacturer would be usefull