Ahr35181
Electrical
- Sep 8, 2003
- 80
Could anybody tell me what the minmium value of insulation resistance an existing 11KV cable should be when tested phase to earth at 5KV test voltage?
We have recently had an 11KV panel off for maintenance, when we came to restore power we tested the panel bus bars & the feeder cable together (as there is a joint in the feeder cable which is suspect).
Red & Blue phases were over 500Mohm to earth & Yellow phase was 130Mohm to earth (similar readings were recorded between phases).
The switchgear is ancient AEI oil filled, & the instruction manuals quote a minimum of 100Mohm to earth at 5KV test voltage.
Do current standards require the same value?
We succesfully restored power but will in due course replace the cable.
We have recently had an 11KV panel off for maintenance, when we came to restore power we tested the panel bus bars & the feeder cable together (as there is a joint in the feeder cable which is suspect).
Red & Blue phases were over 500Mohm to earth & Yellow phase was 130Mohm to earth (similar readings were recorded between phases).
The switchgear is ancient AEI oil filled, & the instruction manuals quote a minimum of 100Mohm to earth at 5KV test voltage.
Do current standards require the same value?
We succesfully restored power but will in due course replace the cable.