Yep we're all talking about the same type of cable - PILC. I know it's normally only screened/shielded at 15kV or above, and belted below that, but screens permit a higher rating, which we have been using. We have had a number of failures in this cable due to either damage during installation (knife nicks to both metalised layer and paper insulation) or just to the screen, and some due to manufacturing defects (as the metalised paper is very thin). Just curious to see if anyone else had experienced similar problems not related to water ingress.
My concern is about the damage leading to localised stress concentrations, which lead to eventual breakdown, as happened in the cases I mentioned above.
We have used MIND cables to minimise impregnant migration, and it seems to have worked well - we have cables up to 70 years old still working well, although we now routinely test the papers whenever we open one up, they are mostly indicating they have many years still to go. Wish new cables were this reliable!
thanks