I have two 125vdc bridge rectifiers that are bieng used to supply a toshiba VCB (125vdc control). One is on the close circuit and the other is on the trip circuit.
Right now we are just doing a point - point on the system. It was found that the rectifier supplying the close circuit (with circuit connected, breaker racked out) measures 166vdc. When the breaker is racked in, the closing coil operates momentarily, and secondary voltage drops to 107vdc momentarily (returns to 166vdc after).
These seems normal to me (besides the 166vdc being slightly high). Problem being, the only things in the circuit are the breaker close circuit, and a GEC instantaneous relay (GEC MCGG instantaneous overcurrent relay)AND WHEN I DISCONNECT THE GEC RELAY THE (REST OF THE CIRCUIT STILL CONNECTED) THE RECTIFIERS SECONDARY VOLTAGE DROPS TO 130VDC...WHICH IS RATED VOLTAGE. This to me doesn't make sense...disconnect a load...and the voltage goes down??? Any suggestions??
Right now we are just doing a point - point on the system. It was found that the rectifier supplying the close circuit (with circuit connected, breaker racked out) measures 166vdc. When the breaker is racked in, the closing coil operates momentarily, and secondary voltage drops to 107vdc momentarily (returns to 166vdc after).
These seems normal to me (besides the 166vdc being slightly high). Problem being, the only things in the circuit are the breaker close circuit, and a GEC instantaneous relay (GEC MCGG instantaneous overcurrent relay)AND WHEN I DISCONNECT THE GEC RELAY THE (REST OF THE CIRCUIT STILL CONNECTED) THE RECTIFIERS SECONDARY VOLTAGE DROPS TO 130VDC...WHICH IS RATED VOLTAGE. This to me doesn't make sense...disconnect a load...and the voltage goes down??? Any suggestions??