All,
I have an existing electrical transformer room with (2) 12kV-277/480V transformers, and I am trying to determine if the room is compliant with NEC 2008. The room is rectangular with a single double door in the middle of the north wall of the room. The transformers sit on either side of the double door with approx. 8' between the two. There is a couple feet of clearance on either end of both transformers. The XFMR are 500KVA and 750KVA.
Would this room require double the work clearance between the two transformers since there is only 1 means of egress? Or is there an exception in Article 450, or elsewhere in the NEC, that would make this installation code compliant?
As always, thanks for the insight.
DJR
I have an existing electrical transformer room with (2) 12kV-277/480V transformers, and I am trying to determine if the room is compliant with NEC 2008. The room is rectangular with a single double door in the middle of the north wall of the room. The transformers sit on either side of the double door with approx. 8' between the two. There is a couple feet of clearance on either end of both transformers. The XFMR are 500KVA and 750KVA.