electricpete
Electrical
- May 4, 2001
- 16,774
Attached is boroscopic picture taken looking into the vent duct area of a 13.2kv motor during teardown inspection following 20 years of service. The motor passed a dc step voltage test to 32kvdc with no non-linearity.
The motor has Thermalastic insulation (wound by Westinghouse in 1980’s).
The corona suppression system in the slot is provided by tape (polyester glass tape impregnated with carbon).
A red surface coating is applied over all.
The photo shows apparent white residue from partial discharge.
The red outer coating is missing.
What is visible appears to be glass type tape, but there is no hint of carbon black material.
That is the real puzzle... how can there be no carbon showing in this photo?
=====================================