Do 13.8 kV overhead line needs ground fault protection per NEC? This 3 wire O/H ACSR line fed from transformer delta winding (step-up) with no intentional grounding and connected to delta winding at other end (step-down).
No. NEC requirements for GF protection only apply to low-voltage systems. If this is a new system, you may want to reconsider your decision to have it be ungrounded. There are many threads here on concerns with ungrounded systems.