Hey folks, this is for a small cogen plant:
I have a 13.8kV switchgear with a 1200A, 95kV BIL vacuum breaker that feeds a 750kVA dry-type 13.8kV/600V transformer via a short 20' cable run. Vacuum breaker has surge arrestors on the load side.
The upstream supply is two large 10MVA transformers connected to the utility ~500ft away.
I'm trying to make the dry-type transformer as small as possible to fit in our e-house. I noticed I have the option of specifying a 60kV BIL instead of 95kV BIL for the HV winding of the dry-type transformer.
What information do I need to make a reasonable assumption whether the HV winding of the dry-type transformer can be lowered to 60kV (to reduce footprint)?
Short of doing a full-blown insulation coordination study (never seen one done for a small cogen CHP plant like ours), can I make some reasonable assumptions here?
I can provide lots of additional info as needed.
I have a 13.8kV switchgear with a 1200A, 95kV BIL vacuum breaker that feeds a 750kVA dry-type 13.8kV/600V transformer via a short 20' cable run. Vacuum breaker has surge arrestors on the load side.
The upstream supply is two large 10MVA transformers connected to the utility ~500ft away.
I'm trying to make the dry-type transformer as small as possible to fit in our e-house. I noticed I have the option of specifying a 60kV BIL instead of 95kV BIL for the HV winding of the dry-type transformer.
What information do I need to make a reasonable assumption whether the HV winding of the dry-type transformer can be lowered to 60kV (to reduce footprint)?
Short of doing a full-blown insulation coordination study (never seen one done for a small cogen CHP plant like ours), can I make some reasonable assumptions here?
I can provide lots of additional info as needed.