13 R heads in closets

Status
Not open for further replies.

coarts

Mechanical
Dec 15, 2006
24
0
0
US
13 R has an exception for installing heads in closets only accessible from outside an apartment [such as from a balcony] with no unprotected openings into the apt. [6.9.7 of nfpa 13r 2007] However, 6.9.4 says if it has heating equipment in it, it gets sprinklered. Do you normally put a sprinkler in outside utility closet or not?
 
Replies continue below

Recommended for you

Sprinkler heads are NOT required in the exterior closet if it meets the requirements of 6.9.7.
The 2010 edition explain better and adds in the 6.9.4 reference(except as permitted by 6.9.7.)

The reference numbers in 2010 are a bit different than 2007. (6.6.4 & 6.6.7)

J. Moore
NICET III - Water Based
 
Be sure to check local fire codes and their amendments. We require sprinklers in all exterior closets of Type III and V construction as defined by the 2012 IBC in Group R occupancies.
 