In the corridor, they have a sheet rock enclosure walls and ceiling.
Below the sheet rock about two feet they installed wood 2X4's across the corridor and the length of the corridor. Than they will attach sheet rock to the bottom of the 2x4's
In this void area is duct and can lights.
Would under 6.8.5 nfpa 13R 2002 require sprinklers in the void area, or would you call it limited combustible, ot something close to 6.8.5 langage??
6.8.5 Sprinklers shall not be required in attics, penthouse equipment rooms, elevator machine rooms, concealed spaces dedicated exclusively to and containing only dwelling unit ventilation equipment, crawl spaces, floor/ceiling spaces, elevator shafts, and other concealed spaces that are not used or intended for living purposes or storage and do not contain fuel-fired equipment.
Below the sheet rock about two feet they installed wood 2X4's across the corridor and the length of the corridor. Than they will attach sheet rock to the bottom of the 2x4's
In this void area is duct and can lights.
Would under 6.8.5 nfpa 13R 2002 require sprinklers in the void area, or would you call it limited combustible, ot something close to 6.8.5 langage??
6.8.5 Sprinklers shall not be required in attics, penthouse equipment rooms, elevator machine rooms, concealed spaces dedicated exclusively to and containing only dwelling unit ventilation equipment, crawl spaces, floor/ceiling spaces, elevator shafts, and other concealed spaces that are not used or intended for living purposes or storage and do not contain fuel-fired equipment.