1
- #1
TravisMack
Mechanical
- Sep 15, 2003
- 1,757
I'm not really sure where to put this one and how to title it, but thought I would share an experience that I have been running through the last couple weeks.
I quoted a design job for a senior living residential facility. The architect and engineer call out an NFPA 13 system because the architect used the area
increase allowance in the building code. Everything was all fine during the quotation process. The project was awarded.
Then the GC asks all of the subs for value engineering price reductions because the project is over-budget. The fire protection contractor that hired me offered
the GC a VE fee reduction to go with an NFPA 13R system because it is a residential building, 4 stories or less in height. The cost savings was substantial,
so of course the GC thinks this is a great idea.
I get the notice from my customer that we are changing to a 13R system design. I have multiple discussions with the customer that this is not permitted because
of the area increase and not all residential buildings 4 stories or less are 13R. They state that in their area it is fine, because things are just different
in their area. I am also told that even if the mechanical engineer that specifies things is wrong, then you have to follow the criteria anyway. I remind them
that that EOR did not change the criteria. The fire protection contractor salesman offered a VE savings because he was possibly unaware of the IBC criteria for
area increases.
After much back and forth, I had to decide to walk away from the job. There is no project worth putting my business and family security on the line because some
one made an honest mistake and wants everyone to just go along with it so the project can proceed.
I guess this was just more of a rant. With the recent thread about starting up freelance design, this is the stuff you will come across. Not all residential buildings
can be 13R. When the architect and EOR both state 13 is required, the salesman should probably not offer a VE to 13R just to save some dollars. And finally, sometimes you
just have to walk away from a job because of your morals and ethics. This is a large contractor that I have done work for in the past. I may or may not ever get work
from them again because me walking away puts them in a bind. But, I can at least feel good in that I would not compromise to design a system wrong simply for monetary gain.
I will say, however, that over the years, I have had more contractors thank me for pointing out issues like this. Some of them have had to walk from jobs as well because of
improperly specified criteria. So, most will respect you for taking the high road and doing what is morally and ethically correct. They also know that you will not cut
corners just to save a few $$ on their jobs either. I just never want to be in a position to be deposed on a lawsuit and some one asks me under oath if I knowingly and
willingly did something that I knew was wrong for the sake of a project. We all make mistakes, but you can't willingly do the wrong thing.
Travis Mack
MFP Design, LLC
"Follow" us at
I quoted a design job for a senior living residential facility. The architect and engineer call out an NFPA 13 system because the architect used the area
increase allowance in the building code. Everything was all fine during the quotation process. The project was awarded.
Then the GC asks all of the subs for value engineering price reductions because the project is over-budget. The fire protection contractor that hired me offered
the GC a VE fee reduction to go with an NFPA 13R system because it is a residential building, 4 stories or less in height. The cost savings was substantial,
so of course the GC thinks this is a great idea.
I get the notice from my customer that we are changing to a 13R system design. I have multiple discussions with the customer that this is not permitted because
of the area increase and not all residential buildings 4 stories or less are 13R. They state that in their area it is fine, because things are just different
in their area. I am also told that even if the mechanical engineer that specifies things is wrong, then you have to follow the criteria anyway. I remind them
that that EOR did not change the criteria. The fire protection contractor salesman offered a VE savings because he was possibly unaware of the IBC criteria for
area increases.
After much back and forth, I had to decide to walk away from the job. There is no project worth putting my business and family security on the line because some
one made an honest mistake and wants everyone to just go along with it so the project can proceed.
I guess this was just more of a rant. With the recent thread about starting up freelance design, this is the stuff you will come across. Not all residential buildings
can be 13R. When the architect and EOR both state 13 is required, the salesman should probably not offer a VE to 13R just to save some dollars. And finally, sometimes you
just have to walk away from a job because of your morals and ethics. This is a large contractor that I have done work for in the past. I may or may not ever get work
from them again because me walking away puts them in a bind. But, I can at least feel good in that I would not compromise to design a system wrong simply for monetary gain.
I will say, however, that over the years, I have had more contractors thank me for pointing out issues like this. Some of them have had to walk from jobs as well because of
improperly specified criteria. So, most will respect you for taking the high road and doing what is morally and ethically correct. They also know that you will not cut
corners just to save a few $$ on their jobs either. I just never want to be in a position to be deposed on a lawsuit and some one asks me under oath if I knowingly and
willingly did something that I knew was wrong for the sake of a project. We all make mistakes, but you can't willingly do the wrong thing.
Travis Mack
MFP Design, LLC
"Follow" us at